Ceiling fan installation from hell
Old 10-31-2013, 02:48 PM   #1
Thinks s/he gets paid by the post
 
Join Date: Aug 2004
Location: Houston
Posts: 1,448
Ceiling fan installation from hell

I am not an electrician but I have replaced ceiling fans before and never had a problem, until today.

I am replacing a ceiling fan/light on the 2nd floor in my 1965 house. The old fan/light appeared to be original and it had a strange fan speed control box mounted on the wall that had what looked like a transformer block wired to the speed knob. There was no wall switch for the light, you had to use the pull cord.

My plan was to install a new fan/light, install a wall on/off switch where the speed control used to be, and put both the fan and lights on one circuit (so the wall switch could turn the entire system off, not just the fan).

I bought a new Hunter ceiling fan/light (~$100) and installed it. It came with a wireless remote for speed/light but I didn't want that so didn't wire it in. I directly connected the black house wire (hot) to the black fan wire and the striped light wire, and then connected the white fan wire to the white house wire.

I turned the breaker on and went back to the fan. The fan works. The lights work. Literally a minute after I turned it on, one of the 14W CFLs that came with the fan pops and goes dead. 2 minutes later, another one pops. I figure they were cheap and maybe got banged around in transit so got some other CFLs from other fans in my house and put them in. Within 5 minutes 3 more CFLs popped and went dead.

I thought maybe the fan needed the remote control box installed between the house power and the fan/lights, so I wired it in per the instructions. When I turned the power on, the remote control box popped and the side where the wires is turned black. Nothing on the fan works. Time to reassess.

Clearly something is very wrong here. I have multiple other (newer) ceiling fan/lights in my house and they work fine. Some have CFLs, others have incandescents. Could this particular line be wired for more than 120V? Is there a reason the fan and lights need to be on a separate circuit (I think they're all 10A)? I don't have a multimeter but need to get one. I already threw the old fan and speed control away so can't check them for details.
soupcxan is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 10-31-2013, 02:53 PM   #2
Moderator Emeritus
aja8888's Avatar
 
Join Date: Apr 2011
Location: Conroe, Texas
Posts: 18,727
You can get a multimeter at Home Depot for under $20. Where is the ground wire in the light wiring? Or is the house so old it has no common grounds? The white wire should be neutral.

In some of the old houses I have worked on, the ground wires were attached to the metal fixture boxes and not the devices (plugs, etc).
__________________
*********Go Yankees!*********
aja8888 is offline   Reply With Quote
Old 10-31-2013, 03:03 PM   #3
Thinks s/he gets paid by the post
 
Join Date: Jul 2012
Location: Mississippi
Posts: 1,894
Get the multimeter for sure, they are invaluable for figuring this stuff out.

Here's a thread with a similar question, consensus is the bulbs are at fault.

Light Bulb Blowing Immediately - DoItYourself.com Community Forums
rbmrtn is offline   Reply With Quote
Old 10-31-2013, 03:07 PM   #4
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
ls99's Avatar
 
Join Date: May 2008
Posts: 6,506
Funnystory, may be relevant to OP's problem. I recall years ago a Vietnamese family having problems keeping light bulbs in a hallway fan/light fixture. The bulb burned out and they replaced it. As soon as the switch was flipped on, the bulb blew. After several bulbs wewre trashed they decided help was needed.

A friend who employed the couple at her house asked me to see if I could remedy the problem. Finding my way into the seedier parts of Philadelphia, found their home.

A quick check with a voltmeter identified the problem. The fan and light socket were wired for 220 VAC. I told papasan to go to a commercial electrical house and get a 220 volt bult. His English was poorer than my Vietnamese. I wrote a note for what he needed, and after some haggling at the electrical shop they finally sold him a 220 volt bulb.

All was well thereafter...
__________________
There must be moderation in everything, including moderation.
ls99 is offline   Reply With Quote
Old 10-31-2013, 03:11 PM   #5
Gone but not forgotten
imoldernu's Avatar
 
Join Date: Jul 2012
Location: Peru
Posts: 6,335
Try this:
Hot/Ground Reversed - Self Help Forums

Had this problem myself when I wired my shop.

Will be watching, as I'm getting ready to do the same.
__________________
If you want others to be happy, practice compassion. If you want to be happy, practice compassion.
--Dalai Lama XIV
imoldernu is offline   Reply With Quote
Old 10-31-2013, 07:21 PM   #6
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 26,889
Agreed on the meter. On any wiring that you aren't 100% certain of (and since you ripped out old wiring, this qualifies as 'uncertain') you want to check that:

Hot-Neutral = 120V
Neutral-Ground = 0V
Hot-Ground = 120V

It is good to double check all of that with wires attached to a standard incandescent light bulb. These will load the circuit, where as the meter is high impedance and just senses the voltage w/o loading it like the actual appliance will.

-ERD50
ERD50 is online now   Reply With Quote
Old 10-31-2013, 07:46 PM   #7
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
JoeWras's Avatar
 
Join Date: Sep 2012
Posts: 11,702
Lighting circuits can be tricky, especially in older homes where it was common to have the hot feed go directly to the fixtures on the circuit, each fixture then controlled by a drop to the switch. If the drop to the switch is romex or BX cable, they use the white. In this case, many times the "white" wire on the switch leg means nothing since it just interrupts the hot. So, you have to be careful. When this is done, it is supposed to be marked with tape or black marker, but that frequently fades, falls off, or was never done. Let me reiterate. In this kind of circuit, the white is hot. Yes it is. Be careful.

This is a nice little simple reference of two simple wiring methods for lighting: Wiring a Light Switch : Electrical Online

I always have my testers ready. First my simple "bug light", and then the DVM. It would be really unusual to have 240 to a light switch, although this could theoretically happen if for some reason two different hot circuits of the split phase power came into the box. Yikes! But, hey, anything is possible in a 1965 house, especially if there have been a lot of cooks in the wiring through the years.
JoeWras is offline   Reply With Quote
Old 10-31-2013, 07:47 PM   #8
Thinks s/he gets paid by the post
 
Join Date: Aug 2004
Location: Houston
Posts: 1,448
Quote:
Originally Posted by ERD50 View Post
Hot-Neutral = 120V
Neutral-Ground = 0V
Hot-Ground = 120V
Here is what I can confirm using the highly scientific "does it zap my finger" test:

Wall switch OFF (this is a new switch so know it works)
Hot-Neutral = ok.
Neutral-Ground = ok.
Hot-Ground = Ow!

Wall switch ON
Hot-Neutral = Double-OW!
Neutral-Ground = ok.
Hot-Ground = OW!

I can't precisely estimate the voltage until Amazon delivers my multimeter, but I would say the pain feels worse between the hot-neutral with the wall switch on...[puts flame suit on]...

Oh, and I found a picture of the old fan's voltage regulator (a similar one anyway).
Attached Images
File Type: jpg 045_zps4e67125a.jpg (60.7 KB, 6 views)
soupcxan is offline   Reply With Quote
Old 10-31-2013, 08:26 PM   #9
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 26,889
Quote:
Originally Posted by JoeWras View Post
... It would be really unusual to have 240 to a light switch, although this could theoretically happen if for some reason two different hot circuits of the split phase power came into the box. Yikes! But, hey, anything is possible in a 1965 house, especially if there have been a lot of cooks in the wiring through the years.
That is exactly what I suspect - two hots. Like you said, if they used a white as a hot, and that is on the other phase from the black, you'd have 220V.

-ERD50
ERD50 is online now   Reply With Quote
Old 11-01-2013, 06:46 AM   #10
Moderator
Walt34's Avatar
 
Join Date: Dec 2007
Location: Eastern WV Panhandle
Posts: 25,340
I ran into that issue when I was doing residential A/C service work for a national retailer. Customer buys a 5,000 btu 120v A/C, plugs it in. Runs five minutes and fan quits. I came out on the warranty call, fan motor is open, I replace it. Runs for five minutes, then quits. Hmmm.

Having noticed that there wasn't the usual difference in fan speeds (hi, med, low) the light in my head goes on and I check the wall outlet voltage. Yup, 220V. Told customer to call an electrician, and oh, the next fan motor is not covered under warranty and I cannot promise that the compressor is not damaged.

No one back at the shop had ever heard of that happening. Now I guess I know.
__________________
When I was a kid I wanted to be older. This is not what I expected.
Walt34 is offline   Reply With Quote
Old 11-01-2013, 06:55 AM   #11
Thinks s/he gets paid by the post
GalaxyBoy's Avatar
 
Join Date: Jul 2009
Location: The Beautiful Blue Ridge Mountains
Posts: 2,791
Quote:
Originally Posted by Walt34 View Post
I ran into that issue when I was doing residential A/C service work for a national retailer. Customer buys a 5,000 btu 120v A/C, plugs it in. Runs five minutes and fan quits. I came out on the warranty call, fan motor is open, I replace it. Runs for five minutes, then quits. Hmmm.

Having noticed that there wasn't the usual difference in fan speeds (hi, med, low) the light in my head goes on and I check the wall outlet voltage. Yup, 220V. Told customer to call an electrician, and oh, the next fan motor is not covered under warranty and I cannot promise that the compressor is not damaged.

No one back at the shop had ever heard of that happening. Now I guess I know.
I once owned an old house where when I went to sell it, the purchaser's inspector noted that an outlet in the dining room was bad (I don't recall what the tester showed). It turned out to be 220V on a 110V outlet. Good thing we never tried to use that one. My theory is that there was once a window air conditioner at that location, and an owner before me didn't want to bring attention to the fact that the AC didn't work so good in that room, so he got rid of the window-rattler and switched out the outlet to camouflage it.

I guess my only point is that you just can't assume previous owners of older houses haven't done just the most stupid things.
GalaxyBoy is offline   Reply With Quote
Old 11-01-2013, 07:32 AM   #12
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
JoeWras's Avatar
 
Join Date: Sep 2012
Posts: 11,702
Wow. This is so incredible to hear about some of these wiring faults. Scary stuff.

A good home inspector will open the panel and check that all circuits are properly connected. It should be easy to see this mischief at the main panel on most romex wired homes.

Some areas of the country still require conduit in the home. If done right, this is the best way to wire. However, you can really create some crazy circuit issues with that flexibility.

I'm still shaking my head over someone swapping out a 110 outlet on a 220 circuit. Wow.
JoeWras is offline   Reply With Quote
Old 11-01-2013, 08:44 AM   #13
Thinks s/he gets paid by the post
Redbugdave's Avatar
 
Join Date: Apr 2006
Location: Columbia, SC
Posts: 1,132
Our house is a 70s built ranch style which we bought about 20 years ago. I got a good deal on the house back then. That's because it was mish mashed together like you guys have been noting. I am pretty good at working on stuff, and spent the first couple years redoing everything to make it right, and bring it up to code. Actually, I would be surprised if there was any real building codes in SC back then. I redid the wiring, plumbing, added wall sockets, etc.

Bottom line...I am continually surprised at the way people live and the half-assed way they do things. A lot of ignorance and cheap skates out there. I guess the two go together. I don't know why there are not more house fires.
__________________
"I either want less corruption, or more chance to participate in it." Ashleigh Brilliant
Redbugdave is offline   Reply With Quote
Old 11-01-2013, 07:57 PM   #14
Thinks s/he gets paid by the post
 
Join Date: Aug 2004
Location: Houston
Posts: 1,448
Fluke confirms: 240V hot to neutral. No wonder it hurt so much. Somehow the neutral I picked up from the fan switch must be out of phase with the other hot. But that's a new one on me.
soupcxan is offline   Reply With Quote
Old 11-01-2013, 08:00 PM   #15
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
NW-Bound's Avatar
 
Join Date: Jul 2008
Posts: 35,712
Speaking of DVM, I have several high-quality ones, but could not resist picking a cheapo one up at HarborFreight today.

Cost: free with a coupon sent in the mail. Often on sale at random prices from $2.99 to $5.99.
NW-Bound is offline   Reply With Quote
Old 11-02-2013, 11:40 AM   #16
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 14,328
Quote:
Originally Posted by NW-Bound View Post
Speaking of DVM, I have several high-quality ones, but could not resist picking a cheapo one up at HarborFreight today.

Cost: free with a coupon sent in the mail. Often on sale at random prices from $2.99 to $5.99.
I have a bunch of these. It is convenient to be able to measure voltage and current at multiple places at a time when I'm playing with a circuit. Definitely worth the price (free).
travelover is offline   Reply With Quote
Old 11-02-2013, 11:43 AM   #17
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 14,328
A bad common connection will give you different voltages on each leg of the circuit. My garage has 220 volt wiring for a welder, so I added a small breaker box to further break it into two 20 amp circuits for my 110 volt power tools. I made a poor common connection and got some crazy high voltages on one leg until I figured out my mistake.
travelover is offline   Reply With Quote
Old 11-03-2013, 07:30 AM   #18
Thinks s/he gets paid by the post
 
Join Date: Aug 2004
Location: Houston
Posts: 1,448
When I checked the ceiling box, there are 3 sets of wires (I call them pair but they include a copper ground wire) plus 1 extra black wire by itself.

Pair 1 - runs to wall switch, no current
Pair 2 - house power, 120V
Pair 3 - connects to additional outlets in the next bedroom, no current
Extra black wire - 120V to ground or common on the other wires, however also measures 120V to hot from pair 2. When combined with pair 2 this wire gets to 240V which is why my light bulbs were blowing.

I have no idea where this "spare" hot wire is coming from. All the other wires in the house I've seen so far have been romex with white/black/copper. I capped/taped the extra wire and put it back in the box.
soupcxan is offline   Reply With Quote
Old 11-03-2013, 09:21 AM   #19
Thinks s/he gets paid by the post
tryan's Avatar
 
Join Date: Mar 2005
Posts: 2,603
Those bulbs can not be dimmed ... hence the fan switch blows them.
__________________
FIRE'd since 2005
tryan is online now   Reply With Quote
Old 11-03-2013, 09:59 AM   #20
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
NW-Bound's Avatar
 
Join Date: Jul 2008
Posts: 35,712
Quote:
Originally Posted by travelover View Post
I have a bunch of these. It is convenient to be able to measure voltage and current at multiple places at a time when I'm playing with a circuit. Definitely worth the price (free).
You're my man! It's even worth the $2.99 or the $3.99 or whatever.

However, one would need cords with a banana plug on one end and a clip on the other to set up several meters for instrumentation. These can cost more than the DVM if one does not know where to shop (Well, everything costs more than $0!). Of course, ebay comes to the rescue.

Quote:
Originally Posted by soupcxan View Post
...
When combined with pair 2 this wire gets to 240V which is why my light bulbs were blowing...
As we know, there are 2 hot lines carrying 110-120V into the home. Being out-of-phase, they are 220-240V between themselves, and that's what powers the heavy loads such as water heater, clothe dryer, AC, range/oven, etc...

For the rest, usually the outlets for appliances are powered with one circuit, while the lights are powered with another circuit. This is so that if the missus blows the breaker that powers her hair dryer, it would not also take out the bathroom light fixture and leaves her in the dark raving mad.

So, the two hot lines are both brought into the home, as distributed by the two banks of breakers inside the main panel. However, the circuits from the breakers are separate, and one does not have 220-240V except for the intended loads.

Somehow the guy before you managed to crosswire two different circuits, and to bring both of them up to the fan!
NW-Bound is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Quick Links

 
All times are GMT -6. The time now is 09:12 AM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.