Quote:
Originally Posted by bld999 View Post
Making the existing system pull it's weight and get the job done is priority, but if it won't work, I have seen these recommended:

Cost Effective Heater | Comfort Cove | Radiant Systems

Wiring would be needed, of course.

Thanks... but I would like to stay away from electric as a main source.... I have been using one downstairs before, and it will only give a degree or two as we have a big area to heat... and I do not want to be running two electric heaters...
__________________

__________________
Texas Proud is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 02-12-2014, 11:11 AM   #22
Thinks s/he gets paid by the post
 
Join Date: Jul 2010
Location: Chicago
Posts: 1,001
Quote:
Originally Posted by Texas Proud View Post
I do not see where the placements make a difference if they have adjusted the ducts correctly.... IOW, if I only have ducts going downstairs, I would think that my downstairs would be the hot zone...
Usually, the closest floor to the furnace would naturally heat up the quickest. I'll have to assume the furnace is in the attic. If you shut off all the 2nd fl outlets, the 1st fl would be hotter. You may have a problem w/some duct runs that have separated within the walls and experience higher than normal heat loss. I wonder if the flex duct is even insulated? Duct tape adhesive wears away over time, even HVAC aluminum tape will come off too.
__________________

__________________
Dimsumkid is offline   Reply With Quote
Old 02-12-2014, 11:34 AM   #23
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 13,256
Well, a learning experience....


The latest guy was showing me some of my major problems...

1st, we do not have enough return air... big time...

2nd, the original setup had 3 long runs of 10" that goes across the house to heat up most of the downstairs... he said they should have used one big run and then used a manifold on the other side of the house to go to all the vents...

3rd, just really old ducts that are starting to leak...

4th, kinked ducts that are restricting airflow on some...

last, all of our vents are facing the wrong way.... as he said, you are supposed to have them face the wall and the return will bring the air back into the room... he showed me where the vents are actually facing one of the returns.... said all it is doing is keeping the hot air near the ceiling and being sucked back into the system...


Second group seems a bit more knowledgeable than the first...


I think I am going to try for a third... but might wait to see what their bid is....
__________________
Texas Proud is offline   Reply With Quote
Old 02-12-2014, 11:51 AM   #24
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 18,261
I really question some of these -
Quote:
Originally Posted by Texas Proud View Post
Well, a learning experience....


The latest guy was showing me some of my major problems...

1st, we do not have enough return air... big time... .
So how much return area and how much supply area do you have on each floor?



Quote:
2nd, the original setup had 3 long runs of 10" that goes across the house to heat up most of the downstairs... he said they should have used one big run and then used a manifold on the other side of the house to go to all the vents...
How big is the one 'big one' he suggests? It isn't clear that 3 versus one is a problem, it can even be better - depending on the relative sizes. How much vent area is each 10" duct connected to?

Quote:
3rd, just really old ducts that are starting to leak...
Leaks certainly could be a problem, but where are they leaking? This is more an issue of install quality than age - old ducts should not leak if they were properly installed.

Is the furnace in the attic (you only said you don't have a basement - it still could be floor one or two or attic?)? Is it NG, resistance electric, heat pump electric, other?

Quote:
4th, kinked ducts that are restricting airflow on some...
Well, kinked ducts are never good - but which ones are kinked? - this will tell you a lot about how to minimize the costs to repair this.

Quote:
last, all of our vents are facing the wrong way.... as he said, you are supposed to have them face the wall and the return will bring the air back into the room... he showed me where the vents are actually facing one of the returns.... said all it is doing is keeping the hot air near the ceiling and being sucked back into the system...
I'm not following your description at all. Facing the wall? Can you be more descriptive - where are the supplies, floor - near outside wall or inside wall, on the wall at the bottom, wall top, inside or outside walls? Same Qs for the returns. This might be different on first and second floors.

Quote:
Second group seems a bit more knowledgeable than the first...


I think I am going to try for a third... but might wait to see what their bid is...
I'd want good answers to everything before spending any $.

-ERD50
__________________
ERD50 is offline   Reply With Quote
Old 02-12-2014, 12:47 PM   #25
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2004
Posts: 11,615
Some comments:
Quote:
Originally Posted by Texas Proud View Post
1st, we do not have enough return air... big time...
Return air has been discussed several times in this thread. First, there's absolutely no problem with using undercut doors and a central hallway, etc as a return air "duct". That's the way it is done in 90+% of the rooms in the US, and when it is done like that you >should< feel air rushing under the doors when the system is operation.
I'm wondering how your latest HVAC guy estimated that the return air was insufficient. You can only tell by looking at the rating of the fan and making an estimate of the pressure loss of the return air "duct" system (such as it is). Comparing the area of the supply air and the return air ducts isn't the right way to determine the sufficiency of the return air system. Also, it's very common for stud bays and floor joist bays to be used as return air ducts, unless the guy looked at the system very closely this is easy to miss.


Quote:
Originally Posted by Texas Proud View Post
2nd, the original setup had 3 long runs of 10" that goes across the house to heat up most of the downstairs... he said they should have used one big run and then used a manifold on the other side of the house to go to all the vents...
Sometimes a larger number of smaller ducts is used so that everything fits inside the available joist depth. One big duct or several small ones shouldn't make any difference if they are of the right size. A single larger duct would have slightly less pressure drop and slightly less loss of heat for a given required duct area, but it's not very significant in the big scheme of things, especially if your ducts are smooth metal.

Quote:
Originally Posted by Texas Proud View Post
last, all of our vents are facing the wrong way.... as he said, you are supposed to have them face the wall and the return will bring the air back into the room... he showed me where the vents are actually facing one of the returns.... said all it is doing is keeping the hot air near the ceiling and being sucked back into the system...
I'm not quite following this. It's true that the air from the supply air registers in each room will flow more-or-less directly to the return air point (again, usually an undercut door or to a hallway, but sometimes to a dedicated return air vent). So, it's better that the air cross the room in this process. In a typical room the supply air is directed out into the middle of the room, having the air directed at a nearby wall seems likely to result in the wall getting a rapid buildup of dust/grime.

I really don't like being at the mercy of hired experts. It's tough to separate fact from "rule-of-thumb" from "this is what somebody told me, I just give estimates."
__________________
"Freedom begins when you tell Mrs. Grundy to go fly a kite." - R. Heinlein
samclem is offline   Reply With Quote
Old 02-12-2014, 01:49 PM   #26
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 13,256
To answer the latest questions...

Furnace is in the attic above the second floor..

Return is a 20X25 and a 12X24... or 788 sq. in.

We have 21 vents... most look about 8X12... or 2016 sq. in.. let's round that down to 1900 with the smaller bathrooms...

The fan is sucking in the filter big time... both people have said it is starving for air...

The run in question is going all the way across the attic... say 20 plus feet... you can easily stand in my attic, so there is no space issue.. but, all 3 ducts are exposed to the attic air... so in my thinking I am losing some heat just because of this... I think he said a 16" line... (I think that I might have been wrong... they might be 8"... will have to check)...

Are vents are in the ceilings here... not the floor or walls.. the one guy even said that some older installers say that how they are installed are correct... the one guy said that people are surprised how much better a system works when they turn them around... the cost of doing this is minimal.....




Ducts are not metal.... they are flex...


There are 3 that I know are kinked... the return air and two that are going where the return air is located... they were just laid down and bent down a chase... no support or solid elbow...
__________________
Texas Proud is offline   Reply With Quote
Old 02-12-2014, 03:32 PM   #27
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 18,261
Good comments from samclem (as always). Yes, the ratio of return to supply doesn't tell the whole story, I was just trying to get some scale of comparison to our house.

Quote:
Originally Posted by Texas Proud View Post
The fan is sucking in the filter big time... both people have said it is starving for air...
Hmmm, there should be some more objective measurement of this. I think the pros use a water-column measurement device (manometer).

It could also be that the fan CFM is larger than what you really need, so it is high relative to the ducts, rather than the ducts being too small. I know I've seem some calculation for this on the web somewhere.

Quote:
The run in question is going all the way across the attic... say 20 plus feet... you can easily stand in my attic, so there is no space issue.. but, all 3 ducts are exposed to the attic air... so in my thinking I am losing some heat just because of this...

From your earlier post, I take it these are the three lines that supply the downstairs? By 'exposed to the attic', do you mean they are not insulated? That could sure help explain at least pert of the reason the downstairs is colder than upstairs.


Quote:
Are vents are in the ceilings here... not the floor or walls..
OK, so all the supply vents are in the ceiling? And returns are as described previously - 20X25 at the top of the stairs and a 12X20 downstairs in the ceiling.

I guess I could see how downstairs, the air is flowing from ceiling to mid-wall height, and not really getting the room warmed up that much.

samclem makes a good point about the doors and airflow back to the returns. Often, carpeting gets installed and there isn't good airflow under the door. But having the doors closed, with a good gap at the bottom, would help force the hot air down to that gap, and then up to the return. With the doors open, the air will tend to travel along the ceiling, not really warming the whole room.

In general, you want the heat to enter at the floor, blow across the floor (we use deflectors in our house t help with that), and then it flows up to warm the room as it flows. You are probably optimized for cooling, which would be opposite. I've seen installs where there are two louvered vents in the wall in the same supply duct, one at the top, one at the bottom. Open the top in summer, open the bottom in winter.


Quote:
There are 3 that I know are kinked... the return air and two that are going where the return air is located... they were just laid down and bent down a chase... no support or solid elbow...
Well, if the return ducts are kinked, that sure is a part of your apparent 'starved for air' condition. Can you tell if these are the upstairs or downstairs returns? It sure sounds like this needs to fixed/bypassed. I think I'd get this fixed first and then see how everything acts to avoid unnecessary work.

-ERD50
__________________
ERD50 is offline   Reply With Quote
Old 02-12-2014, 03:48 PM   #28
Thinks s/he gets paid by the post
 
Join Date: Oct 2012
Location: Colorado Mountains
Posts: 2,134
Quote:
Originally Posted by Texas Proud View Post
... the furnace is sucking the air filters strongly.... the guy even said he had not seen one being pulled like this... that is why they are suggesting either one larger return in our game room or three smaller ones in the bedrooms... This only helps on the upstairs... we will have to see what they can do for downstairs...
Why don't you try running without the filter? When my filters get dirty, I start getting the temp diffs you are talking about. If that makes the problem go away, then you could possibly work on putting a larger filter in the vent you have at an angle or find a less restrictive filter.
__________________
Hermit is offline   Reply With Quote
Old 02-12-2014, 07:14 PM   #29
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 13,256
Thanks for all the help....

With them I have been able to make some observations...

The ducts are getting old and the foil is starting to peel on some of them... the last guy said I did not 'need' to replace them all, but it will only get worse..


I have a quote with R-6... but think that it would be better with R-8... comments

As to the comments about return air... all 3 guys have looked at the unit I have (5 ton AC with the right sized blower).... and all have looked at how big the duct work is from the two returns.... all have said that it is not enough... seems to me to be an easy fix to add a return and fix this problem... not much cost...


ERD50... yes, three lines that supply most of the downstairs (are master bedroom is supplied from a separate line and gets plenty of air)... they are 10 or 12 inch lines... they are insulated, but I do not know what R value they have... they run across the attic, one for the kitchen and dining room...another for the living room and breakfast room and a third for the wash room, small toilet and two more in the large living room...
__________________
Texas Proud is offline   Reply With Quote
Old 02-12-2014, 07:48 PM   #30
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2004
Posts: 11,615
Comments:
Quote:
Originally Posted by Texas Proud View Post
The ducts are getting old and the foil is starting to peel on some of them... the last guy said I did not 'need' to replace them all, but it will only get worse..

I have a quote with R-6... but think that it would be better with R-8... comments
I'm just not a fan of the slinky duct. If you can get real metal ducts or at least "ductboard" ones at a reasonable price (i.e. in places with easy access, esp the bigger ducts) I think it would be a smart move. It has less resistance to air flow, it can be cleaned on the inside (if the ductboard is the right kind), and it doesn't sag, kink, collapse.

Insulation: It seldom makes sense to insulate any ducts that are in conditioned spaces. A >great< way to do the ducts in the attic, if it is practical in your case, is to lay them close to the floor and cover them with loose-fill or batt insulation. Just 6 inches heaped on top of the duct = R 18+ at very low cost in materias. And, if there's little insulation between the ducts and the room below, but lots on top, then the air in the ducts will not be nearly as hot in the summer/cold in the winter when the system turns on, which improves comfort. The installers may not like this idea--they want to get the ducts in and scoot as quickly as possible without raking insulation around or shooting more in/hauling batts up there, etc.

I'd probably go with at least R-8 on the ducts just to assure there's no condensation/dripping on the outside during your hot, damp Houston summers. But I'd want to have quite a bit more.

Which ever way you go, the installers should be confident that you know what to look for and will be going up in the attic to see that all the connections are tight, that there's mastic where there should be, etc.

Quote:
Originally Posted by Texas Proud View Post
As to the comments about return air... all 3 guys have looked at the unit I have (5 ton AC with the right sized blower).... and all have looked at how big the duct work is from the two returns.... all have said that it is not enough... seems to me to be an easy fix to add a return and fix this problem... not much cost...
Sounds reasonable. But take a look at the actual size of the last section of return duct that goes into your air handler, and the areas "upstream" of that. There's no point in paying for a bunch of return ductwork/grills if they exceed the size of that final plenum. Obviously there should be some allowances for losses/constrictions through the filters, etc, but you don't want to pay for a new superhighway that really leads to a one-lane road right before your air handler.
__________________
"Freedom begins when you tell Mrs. Grundy to go fly a kite." - R. Heinlein
samclem is offline   Reply With Quote
Old 02-12-2014, 10:53 PM   #31
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 13,256
Quote:
Originally Posted by samclem View Post
Comments:

I'm just not a fan of the slinky duct. If you can get real metal ducts or at least "ductboard" ones at a reasonable price (i.e. in places with easy access, esp the bigger ducts) I think it would be a smart move. It has less resistance to air flow, it can be cleaned on the inside (if the ductboard is the right kind), and it doesn't sag, kink, collapse.

Insulation: It seldom makes sense to insulate any ducts that are in conditioned spaces. A >great< way to do the ducts in the attic, if it is practical in your case, is to lay them close to the floor and cover them with loose-fill or batt insulation. Just 6 inches heaped on top of the duct = R 18+ at very low cost in materias. And, if there's little insulation between the ducts and the room below, but lots on top, then the air in the ducts will not be nearly as hot in the summer/cold in the winter when the system turns on, which improves comfort. The installers may not like this idea--they want to get the ducts in and scoot as quickly as possible without raking insulation around or shooting more in/hauling batts up there, etc.

I'd probably go with at least R-8 on the ducts just to assure there's no condensation/dripping on the outside during your hot, damp Houston summers. But I'd want to have quite a bit more.

Which ever way you go, the installers should be confident that you know what to look for and will be going up in the attic to see that all the connections are tight, that there's mastic where there should be, etc.



Sounds reasonable. But take a look at the actual size of the last section of return duct that goes into your air handler, and the areas "upstream" of that. There's no point in paying for a bunch of return ductwork/grills if they exceed the size of that final plenum. Obviously there should be some allowances for losses/constrictions through the filters, etc, but you don't want to pay for a new superhighway that really leads to a one-lane road right before your air handler.

Thanks for all the comments... very good indeed....


As for the plenum... I am getting a new one... they will be adding a whole house filter... it is supposed to allow better air flow...
__________________
Texas Proud is offline   Reply With Quote
Old 02-12-2014, 10:55 PM   #32
Thinks s/he gets paid by the post
 
Join Date: Mar 2010
Location: Kerrville,Tx
Posts: 2,710
Quote:
Originally Posted by Texas Proud View Post
Thanks for all the comments... very good indeed....


As for the plenum... I am getting a new one... they will be adding a whole house filter... it is supposed to allow better air flow...
In particular if the area of the whole house filter is larger than the sum of the areas of the return grates it should help since you do take the filters out of the return grates as part of the change.
__________________
meierlde is offline   Reply With Quote
Old 02-12-2014, 11:17 PM   #33
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2004
Posts: 11,615
Quote:
Originally Posted by Texas Proud View Post
As for the plenum... I am getting a new one... they will be adding a whole house filter... it is supposed to allow better air flow...
Sounds good. The thick "media filters" do a good job and only need replacing every 6 months or so. And this will give you a chance to ask the installers how big this filter element should/will be. Their answer will be interesting. The largest commonly available filter element is 20" x 25" = 500 sq inches. You already have 740 sq inches of return duct area--if the ducts are the same size as the grills (they may not be). You can see where this is going: if they install this 500 sq inch filter element and you already have 740 sq inches of duct leading to that bottleneck (with its own filter element, adding to the restriction), then adding even more return air ducts before that filter won't improve your system's overall performance. Now, maybe adding a separate new return duct before the filter solves a local problem (distribution, etc), but that would only be the case if you've already got enough supply air to the "trouble spot" and insufficient return air (under doors, through halls, etc). That can happen, but it's not very common if any thought was put into the design of the system in the first place.

Sorry for the long reply.
__________________
"Freedom begins when you tell Mrs. Grundy to go fly a kite." - R. Heinlein
samclem is offline   Reply With Quote
Old 02-13-2014, 06:24 AM   #34
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 13,256
Quote:
Originally Posted by samclem View Post
Sounds good. The thick "media filters" do a good job and only need replacing every 6 months or so. And this will give you a chance to ask the installers how big this filter element should/will be. Their answer will be interesting. The largest commonly available filter element is 20" x 25" = 500 sq inches. You already have 740 sq inches of return duct area--if the ducts are the same size as the grills (they may not be). You can see where this is going: if they install this 500 sq inch filter element and you already have 740 sq inches of duct leading to that bottleneck (with its own filter element, adding to the restriction), then adding even more return air ducts before that filter won't improve your system's overall performance. Now, maybe adding a separate new return duct before the filter solves a local problem (distribution, etc), but that would only be the case if you've already got enough supply air to the "trouble spot" and insufficient return air (under doors, through halls, etc). That can happen, but it's not very common if any thought was put into the design of the system in the first place.

Sorry for the long reply.


Not a problem with long replies...


From what I was told, and am also reading, the whole house filter is less restrictive...

But, thinking about it.... my return air is NOT what I said... I have a 16" round duct and a 10" round duct.... or about 280 return area.... the filter size should not be the determining factor....

This also means that my supply side is calculated wrong as I would have to figure the duct size instead of the register size.... a 4" line can only supply so much no matter what size vent you have....


So, if they add a 25x25 whole house filter (just guessing at this point, I will ask what it is), I can add another 16" return without a restriction....
__________________
Texas Proud is offline   Reply With Quote
Old 02-13-2014, 10:01 AM   #35
Thinks s/he gets paid by the post
DFW_M5's Avatar
 
Join Date: Sep 2003
Posts: 4,980
Quote:
Originally Posted by Texas Proud View Post
We do not have any dampers in the ducts... we have adjusted the outlets in the rooms to try and help as much as we can... still have airflow problems...


At this time, we are only looking at replacing and upgrading what can be done without tearing up walls... I do not want to go to that level....
Its unusual not to have dampers just off the distribution box for balancing purposes. You might want to try installing dampers first, as it is far better than trying to balance with the room dampers.

That said, if you have flexible ducts, the insulation they use for ducting today is far superior to what was used many years ago, so this might be a good upgrade, as would having a return in each room.
__________________
Doing things today that others won't, to do things tomorrow that others can't. Of course I'm referring to workouts, not robbing banks.
DFW_M5 is offline   Reply With Quote
Old 02-13-2014, 10:57 PM   #36
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2004
Posts: 11,615
Quote:
Originally Posted by Texas Proud View Post
From what I was told, and am also reading, the whole house filter is less restrictive...
The thick, pleated media filters (usually 4" or more thick) last a long time and filter the air well and can be less restrictive than a "flat" filter, but they still restrict airflow appreciably compared to having nothing there. So, there's not much to be gained by having return ducts feeding it that are any bigger than the filter size itself (unless the ducts are >very< long or have a lot of losses for other reason--elbows, etc).

Quote:
Originally Posted by Texas Proud View Post
So, if they add a 25x25 whole house filter (just guessing at this point, I will ask what it is), I can add another 16" return without a restriction....
The largest "stock" 4" media filter I know of is 24" x 24", but the biggest one I can easily get at HD or Lowe's near me is 20" x 25". But, as you say, whether the filter is 24" x 24" or 20" x 25", you still might benefit from additional return air ducting size since you haven't reached the limit of the filter size yet.
__________________
"Freedom begins when you tell Mrs. Grundy to go fly a kite." - R. Heinlein
samclem is offline   Reply With Quote
Old 02-15-2014, 03:48 PM   #37
Thinks s/he gets paid by the post
Live And Learn's Avatar
 
Join Date: Feb 2012
Location: Tampa Bay Area
Posts: 1,688
Sorry - didn't read the entire thread in detail, but I have to have my ductwork replaced. 1500 sq ft house with 9 vents. Two quotes - one for $2,000 one for $3,500. Saw your post about $200 - $300 per vent. I knew the second quote was nuts but you just proved it !
__________________
"For the time being no discipline brings joy, but seems grievous and painful; but afterwards it yields a peaceable fruit of righteousness to those who have been trained by it." ~
Hebrews 12:11

ER'd in June 2015 at age 52. Initial WR 3%. 50/40/10 (Equity/Bond/Short Term) AA.
Live And Learn is offline   Reply With Quote
Old 02-19-2014, 10:08 AM   #38
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 13,256
OK, the day is here when I am doing the change...


I was surprised at the 3 quotes... two were very expensive... one over $8K and one over $7K.... the one that seemed the most knowledgeable and the one that did more work to see what I had already came in just under $4K...


I took the low bid... they are certified by Trane and have other certifications that the two high bids did not... they also were telling me some of the positives and negatives of the various decisions which the others were not...

We are getting a zoned system, a whole house filter and new ducts...

I opted out of the wi-fi thermostats as they were going to cost me an additional $175.... not worth it at that price...
__________________
Texas Proud is offline   Reply With Quote
Old 02-19-2014, 10:33 AM   #39
Moderator Emeritus
Bestwifeever's Avatar
 
Join Date: Sep 2007
Posts: 16,372
Thanks for posting this discussion. We have an old house and never know when we might find threads like this helpful!

The low-range costs seem reasonable, TP, and you have certainly done your research!
__________________
“Would you like an adventure now, or would you like to have your tea first?” J.M. Barrie, Peter Pan
Bestwifeever is offline   Reply With Quote
Old 02-19-2014, 10:33 AM   #40
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2004
Posts: 11,615
Quote:
Originally Posted by Texas Proud View Post
.... the one that seemed the most knowledgeable and the one that did more work to see what I had already came in just under $4K...


I took the low bid... they are certified by Trane and have other certifications that the two high bids did not... they also were telling me some of the positives and negatives of the various decisions which the others were not...

We are getting a zoned system, a whole house filter and new ducts...
Sounds like a good choice of contractor. Hopefully the extensive work (and $$) will fix the problem. "Zoned" = multiple air handling units? Sounds like you are getting a good price. Probably not a big deal where you are, but where the weather gets really cold having another source of heat in the house can be a very nice thing.
__________________

__________________
"Freedom begins when you tell Mrs. Grundy to go fly a kite." - R. Heinlein
samclem is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
I want to expand my duct cleaning business...but how? thefed Other topics 5 08-04-2008 09:46 PM
Animal in Heating Duct TromboneAl Other topics 21 10-26-2007 10:11 AM
Duct tape Moemg Other topics 10 08-10-2007 01:51 AM
I just got an opportunity to bid on a $50,000 job!!! Air duct cleaning thefed Other topics 10 06-20-2007 01:36 AM
Duct Cleaning Sundance Kid Other topics 13 06-13-2007 12:27 PM

 

 
All times are GMT -6. The time now is 04:33 AM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.