Old 01-25-2011, 02:38 PM   #21
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,242
Quote:
Originally Posted by TromboneAl View Post
You've got to put a meter on the electric floor. The inline equivalent of a Kill-a-watt. You can turn off everything in the house but the heater and look at your power meter to evaluate how much it's using.



So, you added 3000 KWH in Dec. The intergoogle tells me that "The WarmlyYours electric floor heating system uses 15 watts per square foot." If your heater draws 1500 watts, then that would correspond to it being on for 2000 hours/month or 67 hours per day. Not possible.

So perhaps there's a short somewhere.

15 watts per sq. ft. X 1000 sq ft. = 15,000 not 1,500.. that is 200 hours/month or 6.7 hours per day... which is possible... and might be what is happening if very cold...
Texas Proud is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 01-25-2011, 03:00 PM   #22
Full time employment: Posting here.
 
Join Date: Mar 2008
Posts: 968
dang-- but that still seems unlikely to run that much....
bizlady is offline   Reply With Quote
Old 01-25-2011, 03:35 PM   #23
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
TromboneAl's Avatar
 
Join Date: Jun 2006
Posts: 12,880
Quote:
Originally Posted by Texas Proud View Post
15 watts per sq. ft. X 1000 sq ft. = 15,000 not 1,500.. that is 200 hours/month or 6.7 hours per day... which is possible... and might be what is happening if very cold...

OK, thanks. I had thought the mispost post corrected it to 100 sq ft.
__________________
Al
TromboneAl is offline   Reply With Quote
Old 01-25-2011, 04:05 PM   #24
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,242
Quote:
Originally Posted by bizlady View Post
dang-- but that still seems unlikely to run that much....

I doubt you have a 15,000 watt heater system.. that is over 50,000 BTUs which could heat a small house...

Here is a calculator that says a 10X10 with poor insulation and Michigan winter would only need a 4,000 BTU system....


http://hearth.com/cgi-bin/btucalc.pl
Texas Proud is offline   Reply With Quote
Old 01-25-2011, 04:21 PM   #25
Thinks s/he gets paid by the post
 
Join Date: Jul 2010
Location: Chicago
Posts: 1,008
Bizlady,
Don't think you answered if there was a thermostat controlling the system. If so, is it the Honeywell round mercury type? Check it with a level to see if it was set correctly. If not, it could be running continuously. Had a coworker that had this problem, couldn't believe the heat guys could make 3-4 trips and never checked the level on the thermostat.....I sent him my bill for the fix! The heat company installer was really embarassed.
Dimsumkid is offline   Reply With Quote
Old 01-25-2011, 04:38 PM   #26
Thinks s/he gets paid by the post
 
Join Date: Jun 2006
Posts: 2,083
Bizlady, is this a heat pump or resistive heat?
Our house is set up very similar.
Do they have an off peak meter for the heat pump? If so, what was that meter showing for use in Dec? We tend to be home more in the winter, bake a lot more, and so use more electricity. Our heat pump use has never gone over about 1800 kwh in a month (heat pump and water heater).
Also, if it is a heat pump system, did you say you saw 'pipes'? Was this in the floor itself? Typically the systems I have seem use tubing, generally Pex I think. If you saw copper pipes, that may be something to investigate.
Also, they really should have laid down insulation under the tubing otherwise you would be heating the ground, as others have said. I would guess this would double the bill.

Any details you can provide may be helpful. Good luck!
__________________
"We do not inherit the earth from our ancestors, we borrow it from our children.
(Ancient Indian Proverb)"
Zathras is offline   Reply With Quote
Old 01-25-2011, 05:53 PM   #27
Full time employment: Posting here.
 
Join Date: Mar 2008
Posts: 968
It is tubes and not pipes in the floor.

The unit info is this:
  • Thermolec - Model B-10U-FFB
  • 10 KW
  • 41.6 amps
  • volts/ph/hz - 240/1/160
BTU 34120

It is a boiler I am told-- if that makes sense-- used only for the in-floor heat.

KWH in the home ran about 460 most of the month, and 600 Kwh in the colder winter months- which was before the in-floor hear was hooked up.

This month Kwh bill from Dec is 4750 kwh -- YIKES
bizlady is offline   Reply With Quote
Old 01-25-2011, 06:17 PM   #28
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
ls99's Avatar
 
Join Date: May 2008
Posts: 6,506
Looks like they are using electric heater to run a boiler to heat the liquid circulating in the floor heating piping.

If the they wanted to find the most inefficient method to provide heat, they succeeded.

While having electric resistance wires in the floor would have been bad enough this setup takes the cake.

Edit add: entirely plausible that there is a leak in floor plumbing. Hot water leaking out, the automatic level control adding water to maintain water supply, thus constantly heating cold water to the pre set temperature.

Should find an independent hvac pro. who does not sell anything but his expertise in evaluating the SYSTEM as a whole, including heat load calculations. The electrician will likely verify that electrically the system works. He won't be interested in diagnosing system design or system operation.

Good luck/
__________________
There must be moderation in everything, including moderation.
ls99 is offline   Reply With Quote
Old 01-25-2011, 06:19 PM   #29
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 14,328
Quote:
Originally Posted by bizlady View Post
The unit info is this:
  • Thermolec - Model B-10U-FFB
  • 10 KW
  • 41.6 amps
  • volts/ph/hz - 240/1/160
..........
10 kilowatt heater at ten cents per kilowatt hour costs a buck an hour to run. 720 hours in a month....hmmmm

Seems like house would be sweltering if it ran that much of the time
travelover is offline   Reply With Quote
Old 01-25-2011, 06:44 PM   #30
Thinks s/he gets paid by the post
 
Join Date: Jul 2010
Location: Chicago
Posts: 1,008
Quote:
Originally Posted by travelover View Post
10 kilowatt heater at ten cents per kilowatt hour costs a buck an hour to run. 720 hours in a month....hmmmm

Seems like house would be sweltering if it ran that much of the time
Not so sure that's the case...basement heat will travel upstairs, causing the gas heated system upstairs to fire even less. So what shuts the system off?
Dimsumkid is offline   Reply With Quote
Old 01-25-2011, 09:39 PM   #31
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
Quote:
Originally Posted by ls99 View Post
If the they wanted to find the most inefficient method to provide heat, they succeeded.

While having electric resistance wires in the floor would have been bad enough this setup takes the cake.
Exactly. The only way to make it less efficient would be to dump the hot water out into the creek after it heats the slab (and the rest of the continental plate).

Did the installer pull a permit? MN is a fairly "progressive" state--are there any laws or codes concerning the installation of such systems?

If the system is as you describe/assess (hydronic fluid heated by electric resistance without insulation beneath the slab) I'd guess the best things to consider now would be:
a) If there's sufficient headroom in the basement, put foam insulation atop the slab, hydronic tubes above that, and a floor. Heat the water with natural gas.
b) If there turns out to be insulation under the slab, consider converting to NG heating of the hydronic fluid.
c) Abandon the "warm basement floor" dream and add forced air heat to the basement. Some throw rugs in strategic locations will help keep feet warmer. Wall-to-wall carpets in basements, especially directly atop a slab, are an invitation to mold and uckiness.
samclem is offline   Reply With Quote
Old 01-26-2011, 05:26 AM   #32
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 14,328
Quote:
Originally Posted by Dimsumkid View Post
Not so sure that's the case...basement heat will travel upstairs, causing the gas heated system upstairs to fire even less. So what shuts the system off?
Yes, the heated air would rise, but unless most of the heat is sucked into the ground, the amount of electric heat being generated should just about heat the house.

As a comparison, I did an Manual J calculation for my 2500 square foot house and even at zero degrees outside it only takes 35,000 btus to maintain temperature.
travelover is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
High Battery Cost Curbs Electric Cars ERD50 Other topics 118 11-06-2010 04:29 PM
Electric Bill Suprise RedHawk Other topics 4 04-08-2010 07:03 AM
Reduce electric bill by installing radiant barrier in attic? soupcxan FIRE and Money 102 08-19-2009 08:26 PM
The perils of technology-- got a $200 electric bill this month Nords FIRE and Money 23 05-28-2007 08:00 PM
June Electric Bill IHateCNBC FIRE and Money 57 07-21-2006 04:07 PM

» Quick Links

 
All times are GMT -6. The time now is 03:57 PM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.