Lighting problem, need suggestions

I am going back to the great knowledge base that is here for things besides finance.....


I have a problem that I have been trying to determine what I should do and would like to get some thoughts....


In our kitchen we have 4 pot lights in the ceiling. These were installed by who knows by the previous owner when the kitchen was remodeled. My problem is that two of them get too hot and will turn off after being on for between 15 and 30 minutes. I have changed the lights to a lower wattage and have also installed CFL. They use the large flood light.


I would like to not have to have someone come in and replace them if I do not have to.... but I also do not like them turning out... it does not happen often, but there are times when both of the problem lights are out and they are on the same side of the kitchen....


As an FYI, this is the first floor, but there is no upstairs room over the kitchen, so they are basically in an attic...


Any suggestions of what we can do
Texas Proud is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 03-06-2014, 08:48 AM   #2
Thinks s/he gets paid by the post
 
Join Date: Feb 2012
Posts: 1,495
I've become a big fan of LED's. When redid master bath used some 4" and 6" LED spot type lights, from Lowe's. May work for you (but cannot be on dimmer). I also used LED strips under cabinets from Inspired LED on internet that I'm a big fan of.

The spots are very easy to install. While I did not replace any prior can types, I did replace an incandescent fixture as well as several new places. In your case you would not need to install "boxes" per se, as long as the plate of a new LED would cover the hole. Go to a Lowe's or HD and take a look at what they have and see if they would work.
H2ODude is offline   Reply With Quote
Old 03-06-2014, 09:06 AM   #3
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
ls99's Avatar
 
Join Date: May 2008
Posts: 6,506
THe wonders of recessed lighting. The fixtures have thermal overload cutout switches. The bucket gets too hot, circuit opens. So far they work as intended.

Where the problems come in is if the installed units are not rated for insulation cover. These have lots vent holes that allow hot air to escape to the attic. Along comes new owner with the insulation to try and keep heat in the house.

My house was just like that when we bought it. And had 150W floods in the buckets rated for max 100 watts. And had styrofoam slabs laid over the bucket tops. Can you see the stupidity?

By the way fiberglass insulation does not keep warm air from flowing out. Need solid barrier for that.

Solution: CFL or LED, then get bathroom type snap in glass cover which has seals on the rim to keep airflow out. That is how I solved the problem. I was too lazy and cheap frugal to replace the buckets.
__________________
There must be moderation in everything, including moderation.
ls99 is offline   Reply With Quote
Old 03-06-2014, 09:17 AM   #4
Thinks s/he gets paid by the post
Rustic23's Avatar
 
Join Date: Dec 2005
Location: Lake Livingston, Tx
Posts: 4,204
I have two in the kitchen that did the same thing. Changed the bulbs out to pigtail compact florescence and have had no problem, going on five years and have not had to replace a bulb yet.
__________________
If it is after 5:00 when I post I reserve the right to disavow anything I posted.
Rustic23 is offline   Reply With Quote
Old 03-06-2014, 09:21 AM   #5
Thinks s/he gets paid by the post
 
Join Date: Jul 2012
Location: Mississippi
Posts: 1,894
Sounds like the thermal switch is getting tripped. It could be faulty itself. You said you already tried lower wattage/CFL bulbs. It might be the insulation around the cans. It's not supposed to be piled up around can, needs some space for the heat to escape.

Here's an article with a similar question, Electrical Wiring in the Home: why does my recessed light turn out?, flood lights, heat safety
rbmrtn is offline   Reply With Quote
Old 03-06-2014, 10:41 AM   #6
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 26,895
I agree with the others - go for LED or CFL as those produce less heat for the given light output.

I will go a step further - do not use these lights if they are tripping on/off. That tells you they are getting dangerously hot, and if the trip circuit fails (I really don't think they are designed to operate for many cycles, just an emergency situation), you could have a fire. LED/CFL should solve it for you.

Are those two cycling on/off even after installing a CFL/LED? In that case I agree that the trip switch may be faulty. Sometimes these things can get more sensitive over time and many cycles. I know circuit breakers are like that. Safer to have that than the other way around.

-ERD50
ERD50 is offline   Reply With Quote
Old 03-06-2014, 10:42 AM   #7
Thinks s/he gets paid by the post
Rustward's Avatar
 
Join Date: Apr 2006
Posts: 1,684
I had that happen once and it was simply because blown in insulation had blocked the vents in top of the can (pot).
Rustward is offline   Reply With Quote
Old 03-06-2014, 10:43 AM   #8
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
pb4uski's Avatar
 
Join Date: Nov 2010
Location: Sarasota, FL & Vermont
Posts: 36,374
Would something like this work for you?

__________________
If something cannot endure laughter.... it cannot endure.
Patience is the art of concealing your impatience.
Slow and steady wins the race.

Retired Jan 2012 at age 56
pb4uski is online now   Reply With Quote
Old 03-06-2014, 10:57 AM   #9
Recycles dryer sheets
ducky911's Avatar
 
Join Date: May 2010
Posts: 497
Big fan here on LED conversion....I got mine at Orchard supply hardware store. About 30 dollars a light but no more worries about fire. Kitchen has 6 of them on a dimmer switch. Takes about 5 min (or less)a light to install.
__________________
You've got to ask yourself one question: Do I feel lucky? Well, do ya, punk?
Retired July '11 investments in very low cost index and mutual funds, balance once a year at best.
ducky911 is offline   Reply With Quote
Old 03-06-2014, 11:48 AM   #10
Recycles dryer sheets
 
Join Date: May 2013
Posts: 307
Another big fan of LED lights particularly in spot or flood type application. LED lights generate far less heat that other lights including CFL types. I doubt an LED would trigger the thermal cutoff in your existing fixtures.
__________________
Retired Jan 2014 at 48.
gozer is offline   Reply With Quote
Old 03-06-2014, 12:52 PM   #11
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,242
Thanks for the replies, I will take a look at the LEDs... as mentioned, I already have tried the CFLs without luck... my DW wants them to be able to dim....

They did add a layer of blown in insulation and it is what I thought was the problem. I know there are lights that can live with this, but we do not have them...
Texas Proud is offline   Reply With Quote
Old 03-06-2014, 01:03 PM   #12
Thinks s/he gets paid by the post
 
Join Date: Jul 2012
Location: Mississippi
Posts: 1,894
Quote:
Originally Posted by Texas Proud View Post

They did add a layer of blown in insulation and it is what I thought was the problem. I know there are lights that can live with this, but we do not have them...
You should be able to just move the insulation away from the can and see if that fixes the problem. IC-cans are the ones rated for Insulation Contact
rbmrtn is offline   Reply With Quote
Old 03-06-2014, 01:43 PM   #13
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,242
Quote:
Originally Posted by rbmrtn View Post
You should be able to just move the insulation away from the can and see if that fixes the problem. IC-cans are the ones rated for Insulation Contact

I can't , the lights are in a place in the attic where you need to be nimble to get there... for me, that train left the station a LONG time ago...

But, I might send my son up there to see.... but, the LED looks like a good change anyhow and if it does not require it... that much better...
Texas Proud is offline   Reply With Quote
Old 03-06-2014, 01:45 PM   #14
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 26,895
Quote:
Originally Posted by Texas Proud View Post
Thanks for the replies, I will take a look at the LEDs... as mentioned, I already have tried the CFLs without luck... my DW wants them to be able to dim.... ...
Check that the LEDs you look at are actually lower watts total than the CFLs you replace. LEDs generally are lower watts/Lumen, but I've seen some that are very close to some CFLs.

Offhand though, if you've gone from a 60W 'edison' bulb, to a 14W CFL and are still having problems, I don't know that a 9W LED will get you there.

Were the CFLs you tired dimmable? Maybe if they were not, and they were on a dimmer, they were over-heating?

-ERD50
ERD50 is offline   Reply With Quote
Old 03-06-2014, 02:00 PM   #15
Thinks s/he gets paid by the post
Rustward's Avatar
 
Join Date: Apr 2006
Posts: 1,684
Quote:
Originally Posted by Texas Proud View Post
I can't , the lights are in a place in the attic where you need to be nimble to get there... for me, that train left the station a LONG time ago...

But, I might send my son up there to see.... but, the LED looks like a good change anyhow and if it does not require it... that much better...
Never tried this, but if you think that may be the problem you could try removing the bulb and blowing in air from a compressor or vacuum cleaner.
When I did it, I took a 16ft extension painting pole up there to clear the vents -- saved me 32ft of needing to be nimble.

But new lighting would be better.
Rustward is offline   Reply With Quote
Old 03-06-2014, 02:43 PM   #16
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,242
Quote:
Originally Posted by ERD50 View Post
Check that the LEDs you look at are actually lower watts total than the CFLs you replace. LEDs generally are lower watts/Lumen, but I've seen some that are very close to some CFLs.

Offhand though, if you've gone from a 60W 'edison' bulb, to a 14W CFL and are still having problems, I don't know that a 9W LED will get you there.

Were the CFLs you tired dimmable? Maybe if they were not, and they were on a dimmer, they were over-heating?

-ERD50
Yep, dimmable bulbs... it did take longer to overheat, but they still do...
Texas Proud is offline   Reply With Quote
Old 03-06-2014, 02:50 PM   #17
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,242
Quote:
Originally Posted by Rustward View Post
Never tried this, but if you think that may be the problem you could try removing the bulb and blowing in air from a compressor or vacuum cleaner.
When I did it, I took a 16ft extension painting pole up there to clear the vents -- saved me 32ft of needing to be nimble.

But new lighting would be better.

I was looking at the video and was thinking that I could use some compressed air and see if that works....

I also see some bulbs instead of the replacement that was in the video... I think I will try one bulb first and see how that goes... need to do the air first....

I also MIGHT be able to reach the lights with a pole.... but will do that as a last resort.... if the other works, why do it
Texas Proud is offline   Reply With Quote
Old 03-06-2014, 06:32 PM   #18
Recycles dryer sheets
 
Join Date: Nov 2013
Location: rural rocks and cows area
Posts: 220
You can simply remove the interior of the can by removing 3 sheet metal screws and stick your hand up there and rearrange the insulation to provide adequate heat dissipation.

Are these two lights in a higher part of the ceiling or over the stove, dishwasher or refrigerator area where the ambient temp might be a little higher?

We have had the best luck with the Cree brand LED trims. Good luck!
427Vette is offline   Reply With Quote
Old 03-06-2014, 07:51 PM   #19
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,242
Quote:
Originally Posted by deadshort52 View Post
You can simply remove the interior of the can by removing 3 sheet metal screws and stick your hand up there and rearrange the insulation to provide adequate heat dissipation.

Are these two lights in a higher part of the ceiling or over the stove, dishwasher or refrigerator area where the ambient temp might be a little higher?

We have had the best luck with the Cree brand LED trims. Good luck!

It is actually funny that these are not over the stove... the ones over the stove do not have a problem.... but, there is a possibility that my son's closet is just above the stove and they are between floors...
Texas Proud is offline   Reply With Quote
Old 03-07-2014, 06:07 AM   #20
gone traveling
 
Join Date: Sep 2003
Location: DFW
Posts: 7,586
3 solutions as has already been mentioned, remove insulation from around cans in the attic; or buy insulated cans, or replace bulbs with leds.
eytonxav is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Debt problem or spending problem ? frayne FIRE Related Public Policy 9 03-11-2013 07:00 AM
The “not my problem” mindset is a problem. Midpack Other topics 14 05-01-2012 04:42 PM
Anyone else try 5000k (full spectrum) lighting at home? Walt34 Other topics 5 03-06-2011 12:30 PM
FI/RE a nice problem to have but still a problem Grizz Hi, I am... 27 06-29-2007 01:29 AM

» Quick Links

 
All times are GMT -6. The time now is 01:37 PM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.