Question for Electrical Engineers & Electricians

Sitting at my computer today and about to log on here, and the UPS under the desk suddenly came on and stayed on but the lights hadn't so much as flickered. Hmmm.

The software that normally communicates with it to adjust settings and such had been intermittent for a year or so and finally quit working last month. So I crawl under the desk and start pushing the buttons to see if I can get an inkling as to what is going on and one of the readouts says the input voltage is 143v. What!!!

So I go get my Fluke meter and sure enough, it says the wall outlet is holding steady at 140 vac. This is not good, and I'm debating whether to flip the main circuit breaker to shut off all power to the house. Meanwhile, I'm trying to get the UPS to turn off but the only switch that seems to respond is the one that shows different items like input and output voltage, hertz, and such. I call the power company to let them know and decide that the UPS is shot and I'm going to need a new one so I head out to get that. It is a survivor of a nearby lightning strike a couple of years ago that fried a bunch of other stuff and is so old I have only a vague memory of buying it so I guess I got my nickel's worth. The only way to turn it off was take the batteries out.

By the time we get back home with the new UPS there is a recording from the power company acknowledging that there was a failure in a piece of equipment that regulates voltage. Yeah, I had that part figured out. Rechecked voltage and it is now 116, so okay. Oh, and all the clocks had to be reset so power was off for at least a few minutes.

And the new UPS communicates with the software (I bought the same brand/model since it worked so well for so long).

My question is this: Was the voltage high enough at 140 vac that I should have shut down power to the house or can appliances/lights accept that much and not be damaged?
__________________

__________________
I heard the call to do nothing. So I answered it.
Walt34 is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 10-07-2016, 06:53 PM   #2
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 8,652
Yes, I'd have shut off the power. Sometimes this is caused by a bad neutral wire connection and depending on the load on each side of the transformer, the voltage on one side can shoot up toward 220 volts. I had this happen at a subpanel in my garage and got 170 volts in one outlet.
__________________

__________________
Yes, I have achieved work / life balance.
travelover is online now   Reply With Quote
Old 10-07-2016, 07:46 PM   #3
Moderator
Walt34's Avatar
 
Join Date: Dec 2007
Location: Eastern WV Panhandle
Posts: 14,358
Okay, something to keep in mind for the future if it ever happens again. Thanks.
__________________
I heard the call to do nothing. So I answered it.
Walt34 is offline   Reply With Quote
Old 10-07-2016, 07:48 PM   #4
Thinks s/he gets paid by the post
MooreBonds's Avatar
 
Join Date: Aug 2004
Location: St. Louis
Posts: 1,949
While on the topic of house electric power.....I'll be building a new house next year. I was going to have the electrical contractor install a "whole house surge suppressor"....but is there anything similar to put on the incoming electrical service to possibly regulate the voltage to prevent a spike like that? Or does it mainly only prevent large surges?
__________________
Dryer sheets Schmyer sheets
MooreBonds is offline   Reply With Quote
Old 10-07-2016, 08:04 PM   #5
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 8,652
Here is a technical explanation of what happens when the neutral wire is broken or has a bad connection.
electrical - Power company's neutral cause surges and brownouts? - Home Improvement Stack Exchange
__________________
Yes, I have achieved work / life balance.
travelover is online now   Reply With Quote
Old 10-07-2016, 08:06 PM   #6
Moderator
Walt34's Avatar
 
Join Date: Dec 2007
Location: Eastern WV Panhandle
Posts: 14,358
Quote:
Originally Posted by MooreBonds View Post
While on the topic of house electric power.....I'll be building a new house next year. I was going to have the electrical contractor install a "whole house surge suppressor"....but is there anything similar to put on the incoming electrical service to possibly regulate the voltage to prevent a spike like that? Or does it mainly only prevent large surges?
I know you can buy them for individual outlets, the UPS I have has that feature built in (that's what set it off) but you can buy the device separately, so I imagine there are ways to do that for an entire building. Think of large data centers and the like, I'd think they'd have something like that.

The "whole house surge suppressors" do not prevent a low overvoltage like the one I had because I have one installed. Or at least the one I have doesn't prevent it.
__________________
I heard the call to do nothing. So I answered it.
Walt34 is offline   Reply With Quote
Old 10-07-2016, 08:12 PM   #7
Thinks s/he gets paid by the post
gauss's Avatar
 
Join Date: Aug 2011
Posts: 1,518
Not sure if anyone is using incandescent bulbs any more, but their life can be significant reduced by overvoltage. There is an exponential relationship, to the thirteenth power, that has been observed between voltage and lifetime in incandescents.

-gauss
__________________
gauss is online now   Reply With Quote
Old 10-07-2016, 08:15 PM   #8
Thinks s/he gets paid by the post
JoeWras's Avatar
 
Join Date: Sep 2012
Posts: 1,755
But at least the shavers and cell phones will be OK. They can take the voltage. Who cares about the fridge anyway, as long as you have the cell phone.

Wow, that sounds like a pretty nasty overvoltage event.
__________________
JoeWras is offline   Reply With Quote
Old 10-08-2016, 08:03 AM   #9
Thinks s/he gets paid by the post
DFW_M5's Avatar
 
Join Date: Sep 2003
Posts: 4,699
Sounds like you may need one of these:
https://en.wikipedia.org/wiki/Power_conditioner
but that can be a pretty expensive safety measure, especially for the whole house.
Not sure if the power company may have some liability for such an over voltage situation.
__________________
Doing things today that others won't, to do things tomorrow that others can't. Of course I'm referring to workouts, not robbing banks.
DFW_M5 is offline   Reply With Quote
Old 10-08-2016, 07:58 PM   #10
Recycles dryer sheets
 
Join Date: Oct 2009
Posts: 249
I just installed these at my new house and have used them in the past.
DeltaSurgeProtectors.com - Homepage
__________________
You do not have a soul. You are a soul. You have a body.
folivier is offline   Reply With Quote
Old 10-08-2016, 08:12 PM   #11
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 8,652
Quote:
Originally Posted by folivier View Post
I just installed these at my new house and have used them in the past.
DeltaSurgeProtectors.com - Homepage
There is a difference between a surge or spike and a continuous high voltage. A surge protector is useful, but would not have helped in Walt's case.
__________________
Yes, I have achieved work / life balance.
travelover is online now   Reply With Quote
Old 10-09-2016, 12:03 AM   #12
Thinks s/he gets paid by the post
Sunset's Avatar
 
Join Date: Jul 2014
Location: Chicago
Posts: 2,759
Wow totally amazing.
I think I will get some UPS devices to protect my computers and tv. I had not bothered as I figured I wouldn't lose much if a power failure hit , but I never knew of a power increase to an outlet, that's not a spike.
__________________
Sunset is offline   Reply With Quote
Old 10-09-2016, 07:07 AM   #13
Thinks s/he gets paid by the post
ls99's Avatar
 
Join Date: May 2008
Posts: 4,488
There are several brands of Line Voltage Regulators. One I used in Alaska for the seismic recording sytem was a brand named SOLA. This unit was before the 10KW UPS.

In the remote village electric power was poorly regulated and out as often as on.

Be aware full time power regulators tend to be inefficient, run fairly hot. For whole house 220 it would be a very expensive proposition, both in inital cost and operating losses. The Sola unit was a ferroresonat sytem only running on 117 VAC. It regulated very well, ran hot and very noisy with 60 Hz hum.

As for 140 VAC utility, that is high. Agree, better turn off main breaker.
__________________
There must be moderation in everything, including moderation.
ls99 is offline   Reply With Quote
Old 10-09-2016, 03:24 PM   #14
Moderator
Walt34's Avatar
 
Join Date: Dec 2007
Location: Eastern WV Panhandle
Posts: 14,358
Quote:
Originally Posted by ls99 View Post
As for 140 VAC utility, that is high. Agree, better turn off main breaker.
If it ever happens again that's what I'll do.

Thanks for all the answers guys.
__________________
I heard the call to do nothing. So I answered it.
Walt34 is offline   Reply With Quote
Old 10-09-2016, 08:39 PM   #15
Thinks s/he gets paid by the post
JoeWras's Avatar
 
Join Date: Sep 2012
Posts: 1,755
Wow, timely. We just endured Hurricane Matthew. Shortly after I posted something here about "mostly rain, only breezy," it all went to heck. I jinxed myself.

Tree fell on a feeder line to the neighborhood and we got all sorts of weird power surges for about 2 minutes. It was like a David Lynch movie here. I was on my way down to trip the breaker, when the electric company's equipment did the deed on their end.

There were casualties. I lost an A/C->D/C power adapter. I lost all the recordings on the DVR, and there may be other latent damage. All computers have backup and surge protectors. It is unknown whether they absorbed anything, although the computers survived fine.
__________________

__________________
JoeWras is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Noticed more people holding signs "need work or food" rayinpenn Other topics 3 05-03-2015 03:51 PM
electrical engineers? do you know what this tube is? kitty_37 Other topics 13 04-04-2014 08:50 AM
How about some electrical help from you engineers donheff Other topics 33 12-16-2011 09:00 AM
Any electricians in the house? Maybe just an electro-nerd could help.... thefed Other topics 6 02-10-2007 10:23 PM
Fast question for he electricians Gpax7 Other topics 6 06-04-2006 01:07 PM

 

 
All times are GMT -6. The time now is 06:20 PM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2016, vBulletin Solutions, Inc.