Rewiring Half-Hot Outlet with no Dedicated Hot Line

Related to the mini-tank water heater installation, I now need to rewire the outlet under the sink to have one plug switched and one plug constantly on.

Unfortunately, the wiring was done like this,



and not like this:



As a result, there is no "always on" hot lead at the outlet.

So, I guess that some new wires will need to be run through the wall, and that I should hire an electrician to do this.

Note that the dishwasher doesn't plug in, but has a dedicated wire that disappears behind the cabinets.

An alternative is to dump the garbage disposal, since we rarely use it (we have a septic tank).

Thoughts?
TromboneAl is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 12-12-2013, 10:29 AM   #2
Thinks s/he gets paid by the post
bjorn2bwild's Avatar
 
Join Date: Mar 2013
Location: Western US
Posts: 1,205
Could you run a short extension cord to the dishwasher outlet?
bjorn2bwild is offline   Reply With Quote
Old 12-12-2013, 10:37 AM   #3
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
Yes, the right answer is to pull new wire to that location.

One "very hillbilly" answer is to make one outlet permanently live (by just connecting the black wires that are now switched) and add a switch under the sink for the disposal to control that outlet. Run the wires in conduit inside the cabinet to a surface-mount box just inside the cabinet door. Protect everything with a GFCI outlet or CB.

It wouldn't be very convenient (opening the door and feeling for the switch with wet hands), but if you want to avoid the trouble and expense of pulling wires inside the wall, it would work.

I wouldn't go as "cheap" as to use a wireless switch or a switched extension cord for the disposal. You want very positive control over something as potentially dangerous as a garbage disposal.
samclem is offline   Reply With Quote
Old 12-12-2013, 10:39 AM   #4
Give me a museum and I'll fill it. (Picasso) Give me a forum ...
REWahoo's Avatar
 
Join Date: Jun 2002
Location: Texas: No Country for Old Men
Posts: 50,004
Quote:
Originally Posted by bjorn2bwild View Post
Could you run a short extension cord to the dishwasher outlet?
+1

If you rarely use the garbage disposal you could get an extension with an in-line switch and use this to turn the disposal on/off whenever you do need it.

Edit to add: X-posted with Samclem. Obviously I adhere to the "cheap" side on the International Scale of Frugality.
__________________
Numbers is hard
REWahoo is offline   Reply With Quote
Old 12-12-2013, 11:06 AM   #5
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
NW-Bound's Avatar
 
Join Date: Jul 2008
Posts: 35,712
I have gotten rid of our garbage disposer. Less grease and food scrap going down the drain to clog it up, less Drano to buy, fewer calls to the plumber. YMMV, of course.
__________________
"Old age is the most unexpected of all things that happen to a man" -- Leon Trotsky (1879-1940)

"Those Who Can Make You Believe Absurdities Can Make You Commit Atrocities" - Voltaire (1694-1778)
NW-Bound is offline   Reply With Quote
Old 12-12-2013, 11:17 AM   #6
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
TromboneAl's Avatar
 
Join Date: Jun 2006
Posts: 12,880
Called an electrician, and the rough estimate he gave me was $400.

You cheap hillbillies pointed me in the right direction. With something like this, you wouldn't need to reach under the sink:

Amazon.com: EtekcityŽ Wireless Controlled Electrical Light Switch Socket Outlet with Remote (Battery Included) ZAP 1F: Electronics
TromboneAl is offline   Reply With Quote
Old 12-12-2013, 11:19 AM   #7
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
NW-Bound's Avatar
 
Join Date: Jul 2008
Posts: 35,712
But, but, but...

Quote:
Originally Posted by samclem View Post
I wouldn't go as "cheap" as to use a wireless switch or a switched extension cord for the disposal. You want very positive control over something as potentially dangerous as a garbage disposal.
__________________
"Old age is the most unexpected of all things that happen to a man" -- Leon Trotsky (1879-1940)

"Those Who Can Make You Believe Absurdities Can Make You Commit Atrocities" - Voltaire (1694-1778)
NW-Bound is offline   Reply With Quote
Old 12-12-2013, 11:31 AM   #8
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
TromboneAl's Avatar
 
Join Date: Jun 2006
Posts: 12,880
Even better, I realized I had one of those remotes, I hooked it in and it works perfectly (yes it works for appliances as well as lights).

TromboneAl is offline   Reply With Quote
Old 12-12-2013, 11:40 AM   #9
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
Quote:
Originally Posted by REWahoo View Post
Edit to add: X-posted with Samclem. Obviously I adhere to the "cheap" side on the International Scale of Frugality.
Of course, when I said "cheap" I meant "alternate, less formal wiring standards."

Al, if you are going that route be sure to check the rating on that wireless switch to assure it's up to the task (same amperage/wattage as the garbage disposal).
samclem is offline   Reply With Quote
Old 12-12-2013, 11:41 AM   #10
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
TromboneAl's Avatar
 
Join Date: Jun 2006
Posts: 12,880
Quote:
Originally Posted by samclem View Post
I wouldn't go as "cheap" as to use a wireless switch or a switched extension cord for the disposal. You want very positive control over something as potentially dangerous as a garbage disposal.
Oops, I missed that.

Yes, that's a consideration. If it went on when you are fishing around for something, it would be pretty bad (see Stephen Spielberg's Firestarter).

That would be pretty unlikely, of course, and IF you always turned off the wall switch to the disposal (and water heater) whenever you put you hand in, it would be even more unlikely. Or you never put your hand in...

Hmmm.
TromboneAl is offline   Reply With Quote
Old 12-12-2013, 11:46 AM   #11
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
TromboneAl's Avatar
 
Join Date: Jun 2006
Posts: 12,880
Quote:
Originally Posted by samclem View Post
Al, if you are going that route be sure to check the rating on that wireless switch to assure it's up to the task (same amperage/wattage as the garbage disposal).
Right. The disposal is 6 Amps and the switch is rated up to 12.

It's a neat solution, but since I don't use the GD much, I think I'll just leave it unplugged. If something gets in there, I can always reach under the sink and plug it in for a minute.

Too bad, because it's surprisingly fun to click the wireless remote and have the GD go on. I think humans have an instinctual affinity for action at a distance, related to the development of hunting tools such as the bow and arrow.
TromboneAl is offline   Reply With Quote
Old 12-12-2013, 11:55 AM   #12
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
Quote:
Originally Posted by TromboneAl View Post
It's a neat solution, but since I don't use the GD much, I think I'll just leave it unplugged. If something gets in there, I can always reach under the sink and plug it in for a minute.
Your undersink storage approach must be a lot different from ours. I'd need to tie a rope around my waist so DW could pull me out if I wanted to reach the back for something.
samclem is offline   Reply With Quote
Old 12-12-2013, 12:58 PM   #13
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 26,821
What does it take to pull another wire? We have conduit here, so it's not that hard.

I would not use the remote. I expect it is against code, which I'm pretty sure calls for a switch within X feet of the disposal, for safety reasons. The remote will end up under the cushion of the couch, several rooms away.

Ideally, you would pull that extra wire, and then use a three-way switch, one leg to disposal, one leg to WH. That way, when the disposal is on, the WH is off. Your 6 amp disposal and WH might exceed the breaker rating. Is the DW on that same breaker?

-ERD50
ERD50 is offline   Reply With Quote
Old 12-12-2013, 01:13 PM   #14
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 14,328
I'd pull in a 14/3 wire if it is easy, to make half of the outlet switched and half live. If not easy, I'd go with the under cabinet switch like samclem suggested. You could use a weather proof switch / box if wet hands are a concern.

Greenfield Weatherproof Electrical Box Lever Switch Cover with Single Pole Switch - Gray-KDL1P at The Home Depot
travelover is offline   Reply With Quote
Old 12-12-2013, 06:05 PM   #15
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
TromboneAl's Avatar
 
Join Date: Jun 2006
Posts: 12,880
Quote:
Originally Posted by ERD50 View Post
What does it take to pull another wire? We have conduit here, so it's not that hard.
It would be a major deal here. No conduit that I know of.

Quote:
Originally Posted by ERD50 View Post
I would not use the remote. I expect it is against code, which I'm pretty sure calls for a switch within X feet of the disposal, for safety reasons. The remote will end up under the cushion of the couch, several rooms away.
-ERD50
IF I did it, I would velcro or otherwise attach the remote to the wall near the existing GD switch. Statistic: 6% or lost remotes are found in the refrigerator.

Quote:
Ideally, you would pull that extra wire, and then use a three-way switch, one leg to disposal, one leg to WH. That way, when the disposal is on, the WH is off. Your 6 amp disposal and WH might exceed the breaker rating. Is the DW on that same breaker?
Clever. But the WH is 10 amps. Add the 5 amp GD, and the total is less than the 20 SWD that the circuit breaker is rated for (some light switches are also on that circuit).

Are there any other risks involved in adding the remote?
TromboneAl is offline   Reply With Quote
Old 12-12-2013, 06:55 PM   #16
Thinks s/he gets paid by the post
 
Join Date: Jul 2012
Location: Mississippi
Posts: 1,894
14-3 wire was mentioned. Run that from the switch to the outlet. There is a diagram at the bottom of this link, Switched Outlet To Half-switched - Electrical - DIY Chatroom - DIY Home Improvement Forum
rbmrtn is offline   Reply With Quote
Old 12-12-2013, 07:04 PM   #17
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
NW-Bound's Avatar
 
Join Date: Jul 2008
Posts: 35,712
Problem with running wire is it may involve tearing out the sheet rock then patching it in order to thread the wire through holes drilled in 2x4 studs. There's no conduit used in new homes anymore.
__________________
"Old age is the most unexpected of all things that happen to a man" -- Leon Trotsky (1879-1940)

"Those Who Can Make You Believe Absurdities Can Make You Commit Atrocities" - Voltaire (1694-1778)
NW-Bound is offline   Reply With Quote
Old 12-12-2013, 08:12 PM   #18
Thinks s/he gets paid by the post
MooreBonds's Avatar
 
Join Date: Aug 2004
Location: St. Louis
Posts: 2,179
Quote:
Originally Posted by TromboneAl View Post
Clever. But the WH is 10 amps. Add the 5 amp GD, and the total is less than the 20 SWD that the circuit breaker is rated for (some light switches are also on that circuit).
2 comments on this:

1) NEC requires you to use breakers at 80% of the connected load. That means a 20 Amp breaker should have no more than 16 Amps connected.

2) Don't forget that motor start-up load is not the same as 'average load'. For an example, look at an In-Sink-Erator disposal:

InSinkErator | BadgerŽ 5 | Garbage Disposal Repair

You'll note that it lists the load as "average" load. When an electrical motor first starts up, it draws more current than when after it's running. This surge is often noted as a "start-up draw" or similar wording, provided in the electrical requirements for motors.

So, if you serve the disposal and heater on the same circuit, don't be surprised if it ends up tripping on a regular basis due to the disposal's start-up draw (you'll likely be using the sink with hot water when you turn on the disposal - which would also cause the water heater to kick on). Add in some lights, and before you know it, you can easily exceed the breaker size, depending on how large the start-up current is for the disposal.
__________________
Dryer sheets Schmyer sheets
MooreBonds is offline   Reply With Quote
Old 12-12-2013, 09:10 PM   #19
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
NW-Bound's Avatar
 
Join Date: Jul 2008
Posts: 35,712
If a 14/3 wire can be threaded through, then a 3-way switch can be used to make sure that both cannot be turned on at the same time, as described earlier.

Quote:
Originally Posted by ERD50 View Post
...
Ideally, you would pull that extra wire, and then use a three-way switch, one leg to disposal, one leg to WH. That way, when the disposal is on, the WH is off. Your 6 amp disposal and WH might exceed the breaker rating.
__________________
"Old age is the most unexpected of all things that happen to a man" -- Leon Trotsky (1879-1940)

"Those Who Can Make You Believe Absurdities Can Make You Commit Atrocities" - Voltaire (1694-1778)
NW-Bound is offline   Reply With Quote
Old 12-12-2013, 09:45 PM   #20
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
Quote:
Originally Posted by TromboneAl View Post
Are there any other risks involved in adding the remote?
This isn't the normal thing that is controlled by these temporary wireless switches (a table lamp, etc). If it gets turned on while you are away from the house (RF interference, neighbor on the same freq, etc) the garbage disposal could be running (without water) for a long time. Probably until something starts to smoke.

If the switch works like one I have, there's no distinct "code" for "on" and "off." When the outlet gets a signal, it just changes state. So, in this case, the GD would be "off" 99.99% of the time and any valid signal it received would turn it to "on."

Also: the motor of the GD is fairly close to the receiver. I don't know how well it is shielded and you'd have to experiment a bit (different motor RPMs, etc) to be sure that once the motor is turned on the receiver can still reliably receive the "off" signal from the transmitter over the electronic racket.
samclem is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


» Quick Links

 
All times are GMT -6. The time now is 08:25 PM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.