Shower exhaust going into attic
Old 07-20-2015, 11:15 AM   #1
Administrator
MichaelB's Avatar
 
Join Date: Jan 2008
Location: Chicagoland
Posts: 40,586
Shower exhaust going into attic

I was up in the attic over the weekend and noticed that the exhaust fan from the upstairs shower is vented into the attic. I looked around, there's no sign of any water residue or damage. I thought all exhaust vents had to lead out through the roof or the side of the house, but not in this case.

How does one vent this once the house is built? Does a hole need to be cut in the attic and the shower vent connected to it? Any recommendations or helpful web sites would be appreciated.
MichaelB is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 07-20-2015, 11:19 AM   #2
Give me a museum and I'll fill it. (Picasso) Give me a forum ...
REWahoo's Avatar
 
Join Date: Jun 2002
Location: Texas: No Country for Old Men
Posts: 50,004
Unless you have a very small attic or use that shower fan far more than average I wouldn't worry about it. We have a large attic area and our fans vent only to the attic.
__________________
Numbers is hard
REWahoo is offline   Reply With Quote
Old 07-20-2015, 11:24 AM   #3
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
Big_Hitter's Avatar
 
Join Date: May 2013
Location: Les Bois
Posts: 5,761
^ so do ours
__________________
You can't be a retirement plan actuary without a retirement plan, otherwise you lose all credibility...
Big_Hitter is offline   Reply With Quote
Old 07-20-2015, 11:27 AM   #4
Thinks s/he gets paid by the post
Lakewood90712's Avatar
 
Join Date: Jul 2005
Posts: 2,223
Is this ? a fan forced exhaust, or just a passive screened opening to the attic. If the latter, was typical construction in the 20th century. No need to change it.

Poor practice , IMO, but I have seen a lot of bath exhaust fan ducts terminated in the attic, just under roof whirlly bird ventilators.
Lakewood90712 is offline   Reply With Quote
Old 07-20-2015, 11:27 AM   #5
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
Quote:
Originally Posted by MichaelB View Post
How does one vent this once the house is built?
I've seen this before, and also with clothes dryers. It's not right for all kinds of reasons--it introduces moisture to the attic, it is a way for a lot of warm air to escape into the attic in the winter (24/7--it's a lot of heat loss) if there's no flapper, etc, etc. It's done this way by cheap builders or sometimes by re-roofers who don't want to bother with a boot/stack (the clue is the small hole in the roof deck that is just covered with tarpaper and shingles. "That oughta be okay").

The two proper options for venting are through the roof or with a soffit vent. A soffit vent is just an opening with a cover under the soffit of the roof (under the eaves). From a purely theoretical standpoint, the "through the roof" answer is slightly better, as the warm, moist air from the bathroom is then clear of the attic. Exhausting the air out the soffit means that some of it may come back in through the normal venting of the attic. From a practical standpoint, I like a soffit vent because it is one less hole in the roof to eventually leak.

In either case, you need a duct from the present duct to either the roof deck or out tot he soffit. In either case, insulate ALL the duct that comes into the attic, otherwise the cold attic (in winter) will condense a lot of moisture on the inside of the duct, and it will drip somewhere. If you go for the soffit vent, try for a short "up" length from the bathroom, and a longer sloping "down" length so any condensation will drip out the soffit and not back into your bathroom. Make sure you have a flapper somewhere int here (possibly already integral to your fan unit, but add one if not) to prevent the constant flow of conditioned air from your home into the attic--the flap opens only when the shower fan puts pressure into the line. Smooth duct will flow more air and trap less water than flex duct.

At a bare minimum, move the end of the shower vent duct to a location inside/under an existing roof vent, add insulation to the duct, and assure there's a flapper in there somewhere.

Good luck!
samclem is offline   Reply With Quote
Old 07-20-2015, 11:32 AM   #6
gone traveling
 
Join Date: Sep 2003
Location: DFW
Posts: 7,586
If you have adequate ventilation, I wouldn't worry about it. The venting of bathrooms to the outside is a newer code requirement and many older houses are vented into the attic.
eytonxav is offline   Reply With Quote
Old 07-20-2015, 11:37 AM   #7
Moderator Emeritus
 
Join Date: May 2007
Posts: 12,894
That's how it was in my house too. I added a piece of duct to bring the exhaust closer to the nearest roof vent, just to be on the safe side. But it had been this way for many years and there was no trace of mold in the attic which was also thoroughly vented through the gables.
FIREd is offline   Reply With Quote
Old 07-20-2015, 11:41 AM   #8
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 26,821
I assume this is your Chicago area home?

At least some of the posters saying it's OK do not live in winter climates. They are probably not aware of the issues with warm moist air condensing in a cold attic.

Moisture in a cold attic can be a real problem, and it can get serious. I would get it properly vented.

-ERD50
ERD50 is online now   Reply With Quote
Old 07-20-2015, 11:43 AM   #9
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Location: Lawn chair in Texas
Posts: 14,183
I'd be mildly concerned about a shower vent, but would NEVER vent a dryer into the attic...

Piercing the roof would be the ideal solution, but an eave, soffit, or ridge vent would be reasonable as well.
__________________
Have Funds, Will Retire

...not doing anything of true substance...
HFWR is offline   Reply With Quote
Old 07-20-2015, 11:45 AM   #10
Give me a museum and I'll fill it. (Picasso) Give me a forum ...
REWahoo's Avatar
 
Join Date: Jun 2002
Location: Texas: No Country for Old Men
Posts: 50,004
+1

I know bupkis bout livin' in da cold...
__________________
Numbers is hard
REWahoo is offline   Reply With Quote
Old 07-20-2015, 12:14 PM   #11
Administrator
MichaelB's Avatar
 
Join Date: Jan 2008
Location: Chicagoland
Posts: 40,586
Yes, this is in Chicago, a cold weather climate, and I don't even know bubkis. No worries, all the know-how is right here on the forum.

This is an upstairs shower, the exhaust is a fan. It doesn't get much use during the cold months, so I probably could get by without doing anything, but I'd rather fix it - it the fix can be done by a handyman and not a roofer. My guess is that rules out a new vent in the roof.

That means my choices would be to install a soffit vent or extend the vent in the attic closer to the existing roof vent. In either case, following Samclem's helpful advice. Do I have it right?

And yes, the dryer vents outside - I am forever unclogging the screen.
MichaelB is offline   Reply With Quote
Old 07-20-2015, 12:33 PM   #12
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
If you decide to go with a soffit vent, here's a product available at Menards that has the exterior grill and an included flapper/backdraft preventer. Less than $10 and you can paint it if you don't need/like white. I'd cut some screening and put it inside to keep out even smaller critters.

But you said "upstairs", so that means any soffit is 16-20' up. That's not fun. Going through the roof deck isn't as hard as it sounds, if you have "regular" asphalt shingles: Drill a big hole, jab a sabresaw through and cut the 4" hole, install the stack and boot slid under the shingles, and glop on a bunch of sealant. But, it is another hole.
samclem is offline   Reply With Quote
Old 07-20-2015, 12:59 PM   #13
Full time employment: Posting here.
 
Join Date: Jan 2011
Location: Southern Maine
Posts: 672
When I moved into my current house... The second floor had two bathrooms... the exhaust of the two bathrooms were connected to each other! I corrected that by connecting each through the roof.

If you live in the cold weather I would be especially cautious of venting to the attic, any added heat in the attic raises the possibility of ice dams.
ChiliPepr is offline   Reply With Quote
Old 07-20-2015, 01:16 PM   #14
Thinks s/he gets paid by the post
38Chevy454's Avatar
 
Join Date: Sep 2013
Location: Cincinnati, OH
Posts: 4,354
The key here is to have adequate attic ventilation. Without that and living in cold Chicago winters, you could have condensation issues. Of course that depends on the volume of attic vs the fan/moisture level/time running.

An attic with sufficient ventilation should not have any problems, although I do agree venting to outside is better.
__________________
The problem isn't artificial intelligence, it's natural stupidity.

You can't spend yourself to prosperity.

Semi-Retired 7/1/16: working part-time (60%) for now [4/24/17 changed to 80%]
Retired Aug 2, 2017; age 53
38Chevy454 is offline   Reply With Quote
Old 07-20-2015, 01:24 PM   #15
Moderator Emeritus
 
Join Date: May 2007
Posts: 12,894
Quote:
Originally Posted by MichaelB View Post
Yes, this is in Chicago, a cold weather climate, and I don't even know bubkis. No worries, all the know-how is right here on the forum.

This is an upstairs shower, the exhaust is a fan. It doesn't get much use during the cold months, so I probably could get by without doing anything, but I'd rather fix it - it the fix can be done by a handyman and not a roofer. My guess is that rules out a new vent in the roof.

That means my choices would be to install a soffit vent or extend the vent in the attic closer to the existing roof vent. In either case, following Samclem's helpful advice. Do I have it right?

And yes, the dryer vents outside - I am forever unclogging the screen.
If you do extend the vent, I would recommend using insulation around the duct. The first time I used my bathroom fan with uninsulated duct on a merely crisp Alabama morning, I was greeted with a rain shower in the bathroom as the steam had condensed in the duct and water was flowing back down. In Chicago, you probably hit those temperatures in September.
FIREd is offline   Reply With Quote
Old 07-20-2015, 01:34 PM   #16
Full time employment: Posting here.
 
Join Date: Nov 2008
Location: Louisville
Posts: 601
I had the same problem with the vent over our kitchen range. I had a local remodeler come out and add a vent in the roof. They cut a hole in the roof and installed the vent with flapper I purchased on top of the roof. They sealed the vent with flapper and ran duct from the range vent in the attic to the new roof vent. You can install the roof vent through the existing shingles easily. I don't recall the exact cost. I think labor and material was less than $200. YMMV.
Masquernom is offline   Reply With Quote
Old 07-20-2015, 01:43 PM   #17
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
Big_Hitter's Avatar
 
Join Date: May 2013
Location: Les Bois
Posts: 5,761
how often do you use the exhaust fan in your upstairs shower?
__________________
You can't be a retirement plan actuary without a retirement plan, otherwise you lose all credibility...
Big_Hitter is offline   Reply With Quote
Old 07-20-2015, 01:48 PM   #18
Moderator Emeritus
Bestwifeever's Avatar
 
Join Date: Sep 2007
Posts: 17,773
Our shower vent/exhaust fan just ends in the attic. I guess I'll put that on the list of things to worry about one day, maybe the next time we get a new roof, but so far no issues with it.
__________________
“Would you like an adventure now, or would you like to have your tea first?” J.M. Barrie, Peter Pan
Bestwifeever is offline   Reply With Quote
Old 07-20-2015, 01:51 PM   #19
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
Quote:
Originally Posted by Big_Hitter View Post
how often do you use the exhaust fan in your upstairs shower?
It's of interest, but not the whole story. If there's no flapper/backdraft preventer, more moisture probably goes into the attic through normal stack effect of the inside air the other 23 hours per day than would go there from one wet bathroom. And then there's the heat loss issue, also dependant on a flapper valve.

With a two story, the heat loss through a 4" fan/vent will be larger than in a single story, due to the greater stack effect.
samclem is offline   Reply With Quote
Old 07-20-2015, 01:51 PM   #20
Full time employment: Posting here.
 
Join Date: Mar 2012
Location: seattle
Posts: 646
Quote:
Originally Posted by FIREd View Post
If you do extend the vent, I would recommend using insulation around the duct. The first time I used my bathroom fan with uninsulated duct on a merely crisp Alabama morning, I was greeted with a rain shower in the bathroom as the steam had condensed in the duct and water was flowing back down. In Chicago, you probably hit those temperatures in September.
+1, in any cold-winter climate, the exhaust air needs to be ducted to the outside, and the duct needs to be insulated. An easy way to do that is buy some "flex" ducting to slip over your galvanized smooth ducting. 6" flex fits nicely over 4" round galvanized if put on prior to making the final end connection. It will compress easily in length, so put a few extra feet on and it will compress to fit.

eg: Atco Insulated Flexible Duct, Polyester, 180F 17002512 | Zoro.com
bld999 is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How to remove this Exhaust Fan Cover?? Amethyst Other topics 14 04-12-2015 07:16 PM
Portable air conditioner exhaust connected to dryer vent? Frugalityisthenewblack Other topics 14 02-24-2012 07:34 AM
How clean is your dryer exhaust? Nords Other topics 32 09-14-2008 08:30 PM
Attic Insulation............. FinanceDude Other topics 24 10-21-2006 09:35 PM

» Quick Links

 
All times are GMT -6. The time now is 06:34 PM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.