Water pressure question for bathroom

This is for the engineers, or anybody who knows plumbing...


We are having our bathroom remodeled... we are going 'all out' (well, we did give up the steam unit ).... we will have 4 massage sprays, a normal out of the wall shower head and a rain shower head for DW...

Now, I knew that the 1/2 inch pipe would be useless if we ran all of these at once... so we are paying extra to run 3/4 lines to this shower...


They are putting together a 'jig' for the 4 massage heads using all 1/2 inch pipe... the contractor said it should be fine since the 3/4 is hooked up to these close to where they spray..

So my question... is this true? Will all 4 be able to go at full pressure? IIRC they are rated at 2.5 gals per minute... Or, do I need them to use 3/4 pipe and then convert to 1/2 at each nozzle?
Texas Proud is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 08-11-2017, 04:39 AM   #2
Moderator Emeritus
Ronstar's Avatar
 
Join Date: Aug 2007
Location: Northern Illinois
Posts: 16,599
I read somewhere that straight 1/2" pipe at 45 psi yields 30 gpm. So you should be fine as long as you have good pressure, minimal bends, and little or no filters on your piping.
Ronstar is online now   Reply With Quote
Old 08-11-2017, 06:07 AM   #3
Thinks s/he gets paid by the post
Senator's Avatar
 
Join Date: Feb 2014
Location: Williston, FL
Posts: 3,925
Quote:
Originally Posted by Texas Proud View Post
They are putting together a 'jig' for the 4 massage heads using all 1/2 inch pipe... the contractor said it should be fine since the 3/4 is hooked up to these close to where they spray..

So my question... is this true? Will all 4 be able to go at full pressure? IIRC they are rated at 2.5 gals per minute... Or, do I need them to use 3/4 pipe and then convert to 1/2 at each nozzle?
Will each 1/2" massage head come directly off the 3/4" main run? If so, that is probably the best you can get.

If a massage head shares a 1/2" supply with another head, maybe not as good.
__________________
FIRE no later than 7/5/2016 at 56 (done), securing '16 401K match (done), getting '15 401K match (done), LTI Bonus (done), Perf bonus (done), maxing out 401K (done), picking up 1,000 hours to get another year of pension (done), July 1st benefits (vacation day, healthcare) (done), July 4th holiday. 0 days left. (done) OFFICIALLY RETIRED 7/5/2016!!
Senator is offline   Reply With Quote
Old 08-11-2017, 06:46 AM   #4
Thinks s/he gets paid by the post
 
Join Date: Feb 2012
Posts: 1,495
Would think it would be fine as long as 3/4 delivered to shower. Be more concerned about how far back the 3/4 comes from, as in did they run it all the way back to the 3/4 entrance?
H2ODude is offline   Reply With Quote
Old 08-11-2017, 06:47 AM   #5
Thinks s/he gets paid by the post
 
Join Date: Feb 2012
Posts: 1,495
Well, I guess that would be the hot water heater, not service entrance.
H2ODude is offline   Reply With Quote
Old 08-11-2017, 07:40 AM   #6
Thinks s/he gets paid by the post
 
Join Date: Nov 2013
Posts: 1,048
+1 for senator's comment.
My vote is for a 3/4" jig, necking it down to 1/2" straight off the "manifold". 3/4 x 3/4 x 1/2 Inch Copper Pipe Tees. No harder and only a couple of dollars more to ensure equal pressure to all heads.
NgineER is offline   Reply With Quote
Old 08-11-2017, 07:50 AM   #7
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,239
Quote:
Originally Posted by H2ODude View Post
Would think it would be fine as long as 3/4 delivered to shower. Be more concerned about how far back the 3/4 comes from, as in did they run it all the way back to the 3/4 entrance?
Yes, they ran it back to the water heater.... going to T in on the cold and hot at that point...

The line will be used only for the shower...
Texas Proud is offline   Reply With Quote
Old 08-11-2017, 07:55 AM   #8
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,239
Quote:
Originally Posted by Senator View Post
Will each 1/2" massage head come directly off the 3/4" main run? If so, that is probably the best you can get.

If a massage head shares a 1/2" supply with another head, maybe not as good.
No, the manifold for the 4 massage sprays will be supplied by the 3/4 right at the shower, but it is one connect point that splits to the 4 heads...


I have been reading up on this and it seems like it should work... IOW, the max the heads can do is 10 gpm for the 4 heads and I have read a few sites that say it should be good... the other two shower heads will come off the 3/4... one is a rain head and I have been reading that can be a water hog...
Texas Proud is offline   Reply With Quote
Old 08-11-2017, 08:00 AM   #9
Recycles dryer sheets
 
Join Date: Nov 2014
Posts: 269
We have 3/4 up to a ft or so away from the fixture. The problem I see is the fixture itself. Most fixtures do not allow the flow your most likely looking for.
Hyper is offline   Reply With Quote
Old 08-11-2017, 08:01 AM   #10
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
calmloki's Avatar
 
Join Date: Jan 2007
Location: Independence
Posts: 7,297
Quote:
Originally Posted by NgineER View Post
+1 for senator's comment.
My vote is for a 3/4" jig, necking it down to 1/2" straight off the "manifold". 3/4 x 3/4 x 1/2 Inch Copper Pipe Tees. No harder and only a couple of dollars more to ensure equal pressure to all heads.
Agree with the 3/4x3/4x1/2 Tees at the manifold. Will you have a small pump circulating hot water through the line while it is not in use? We ran 3/4" hot main line and it takes a fair time before exchanging the old cold water for nice hot water. Upstairs bathroom I brush my teeth before shaving and leave the Hot running during. Shoulda put in a pump. Used to it now, and inertia..
calmloki is offline   Reply With Quote
Old 08-11-2017, 08:49 AM   #11
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,239
Quote:
Originally Posted by calmloki View Post
Agree with the 3/4x3/4x1/2 Tees at the manifold. Will you have a small pump circulating hot water through the line while it is not in use? We ran 3/4" hot main line and it takes a fair time before exchanging the old cold water for nice hot water. Upstairs bathroom I brush my teeth before shaving and leave the Hot running during. Shoulda put in a pump. Used to it now, and inertia..

No, that is something that I guess should be a concern, but not much space to get any more stuff in the closet with the hot water heater....

Running the faucet will not work as this is a dedicated line to the shower... the old 1/2 inch will remain for the rest of the bathroom....


Hmm... thinking about it now, this might mean others cannot take a shower at the same time since the 3/4 line will be taking so much of the water... but, now only have 1 kid at home and she can work around it if needed...
Texas Proud is offline   Reply With Quote
Old 08-11-2017, 09:43 AM   #12
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
calmloki's Avatar
 
Join Date: Jan 2007
Location: Independence
Posts: 7,297
Dedicated line to the shower you should be fine - crank all those heads on at once and you will probably get to the hot pretty darn sudden. Nice that the sinks aren't on the same line.
calmloki is offline   Reply With Quote
Old 08-11-2017, 10:22 AM   #13
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,239
Quote:
Originally Posted by calmloki View Post
Dedicated line to the shower you should be fine - crank all those heads on at once and you will probably get to the hot pretty darn sudden. Nice that the sinks aren't on the same line.
LOL....

We will have two valves up front and one in the back...

One runs the 4 massage heads
Second runs the two shower heads with a diverter to choose either or both
Third in the back with a bench with a hand held


Dang fixtures are costing an arm and a leg!!!! DW is going with some expensive German brand that has temp control and water pressure on different handles... the cheaper ones are like the ones in hotels where you just turn one handle to the temp you want and get full blast no matter what volume you might want...
Texas Proud is offline   Reply With Quote
Old 08-11-2017, 05:03 PM   #14
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
calmloki's Avatar
 
Join Date: Jan 2007
Location: Independence
Posts: 7,297
I ran across some Speakman brand heads and installed them after removing the flow restrictors. Very high marks to Speakman for shower pleasure. read some reviews:

https://www.amazon.com/Speakman-S-20...an+shower+head
calmloki is offline   Reply With Quote
Old 08-11-2017, 05:32 PM   #15
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
Obviously, be sure the cold line is also taken care of--esp that you aren't sharing a small-ish line with something upstream (toilet, sink, etc). It sounds like you plan to be using a lot of hot water and have a large hot water line going to the shower. If there's just a 1/2" cold line line, it might work just fine until someone flushes a toilet upstream of it. THEN you'd glad to have those pricey temperature-compensated anti-scald valves.
samclem is offline   Reply With Quote
Old 08-11-2017, 05:36 PM   #16
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,239
Well, the plumbing rough in is done so it is what it is...

We have 3/4 going into the two faucets for the shower heads and massage heads. Then from the faucet it is half inch. I am not sure if they can do 3/4 from the faucet to the heads so that could be the limiting factor.



Good thing we are doing this. The tub was leaking all over the place. The base plate was rotted out along with some other wood that was around. It leaked into my closet and some shirts that were touching the carpet wicked up the water and they were ruined. I never wore those shirts so I never noticed... it was maybe 15 shirts in.... but, that then meant the carpet had mold and had to be replaced....

The increases just keep coming
Texas Proud is offline   Reply With Quote
Old 08-11-2017, 05:40 PM   #17
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,239
Quote:
Originally Posted by samclem View Post
Obviously, be sure the cold line is also taken care of--esp that you aren't sharing a small-ish line with something upstream (toilet, sink, etc). It sounds like you plant to be using a lot of hot water and have a large hot water line going to the shower. If there's just a a 1/2" cold line line, it might work just fine until someone flushes a toilet upstream of it. THEN you'd glad to have those pricey temperature-compensated anti-scald valves.
Paid to have both lines to 3/4... and the lines are dedicated to the shower...

Now, they did use the old 1/2 inch line to the hand held that is in the back... Hmmm, have not looked at how they did that... they went from copper to PEX.....
Texas Proud is offline   Reply With Quote
Old 08-11-2017, 07:28 PM   #18
Full time employment: Posting here.
 
Join Date: Nov 2008
Location: Louisville
Posts: 601
My wife can look at 100 options for any item, and without seeing the prices, decide she has to have the most expensive one. It's an unbelievable talent. I don't know how she does it, but it never fails....
Masquernom is offline   Reply With Quote
Old 08-11-2017, 08:36 PM   #19
Thinks s/he gets paid by the post
 
Join Date: Jan 2015
Posts: 1,539
DW has the same skill, doesn't matter what the potential purchase is, she calls it "the finger" when the price surprises her too.
__________________
Wisdom starts with wonder
KCGeezer is offline   Reply With Quote
Old 08-12-2017, 08:23 PM   #20
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,239
OK, now a problem has shown itself.... what to do??


They had to change out the pipes on the water heater to get the new ones attached... just a bit ago I noticed that water was dripping out the overflow valve.... the likely culprit is that they put on a pipe that restricts water backing up to the cold water line, so higher pressure in the tank...


Is it OK to live with the overflow?

The pipe runs to the outside of the house, so no big deal in that.... but I wonder what else can happen... just starting to read...


BTW, no place to put an expansion tank unless I tear out some shelves that is over the heater.... and the heater is on the floor so replacement means they get ripped out also....
Texas Proud is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Blood Pressure Medicine question rsingh6675 Health and Early Retirement 20 12-01-2012 07:08 AM
Bottled water vs. filtered water summer2007 Other topics 48 11-21-2008 10:35 AM
Bottled water or tap water David1961 Other topics 35 12-05-2007 04:46 PM
Blood Pressure Question DangerMouse Health and Early Retirement 6 04-10-2007 12:40 AM
Your Fantasy Bathroom Danny Other topics 36 10-16-2005 05:27 PM

» Quick Links

 
All times are GMT -6. The time now is 05:42 AM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.