Old 08-09-2017, 09:07 PM   #21
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,242
ERD50....

I bought the variable speed blower also.... you can see the % that the compressor is doing and the fan... many times the fan is only going at 30%.... compressor at 30% to 50%.... it runs slowly but longer...


When we came back from vacation and I turned down the temp, it spooled up to 100% and cooled it down in a reasonable time... it was hot and humid so not in 30 minutes....
Texas Proud is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 08-09-2017, 10:21 PM   #22
Thinks s/he gets paid by the post
 
Join Date: Mar 2010
Location: Kerrville,Tx
Posts: 3,361
Quote:
Originally Posted by ERD50 View Post

Yes, any repairs are likely to be far more expensive. I take it variable speed motors aren't a $100 commodity like my old blower.
I also set the fan to 'circulate' in summer- that ensures that the fan runs at least 30 minutes out of every hour. So it is 'smart', if the A/C is running that much, it doesn't run the fan by itself any extra. That really helps keep upstairs/downstairs even. And 'circulate' is a very low speed, I think it only used ~ 100 watts.


-ERD50

.
Yes I had 2 blowers fail and the place wanted to charge $700 for each blower, but it was under warranty. Since I leave the blowers on circulate, since that eliminates the time during startup when the blower tries to decide which way to turn. Note that if you visit Amazon you may see someone sell the same blower for $350. This was on a mid range unit and not a top of the line unit which has a different presumably more expensive blower.
meierlde is offline   Reply With Quote
Old 08-10-2017, 05:00 AM   #23
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
target2019's Avatar
 
Join Date: Dec 2008
Location: On a hill in the Pine Barrens
Posts: 9,722
Quote:
Originally Posted by Texas Proud View Post
ERD50....

I bought the variable speed blower also.... you can see the % that the compressor is doing and the fan... many times the fan is only going at 30%.... compressor at 30% to 50%.... it runs slowly but longer...


When we came back from vacation and I turned down the temp, it spooled up to 100% and cooled it down in a reasonable time... it was hot and humid so not in 30 minutes....
Also went with VS instead of 2-stage, in two 2.5 ton units. After 18 months, the difference in cost and comfort is noticeable. This is in NJ, where the emphasis is on winter and summer conditions.

Upstairs is about 1/3 of the total S/Ft. In this house, and this area, I have settings which keep upstairs at reasonable temp during the day (78), and this seems to lessen the load for downstairs system. The center of house has a two story cathedral ceiling, and this feature acts like a large chimney. The new systems are more capable of filling the entire house with cool or heated air.

The finished basement does not have registers. I notice that the systems work longer and harder if the basement entry door from inside house is left open.
target2019 is online now   Reply With Quote
Old 08-11-2017, 03:52 PM   #24
Recycles dryer sheets
 
Join Date: Mar 2014
Location: Annapolis
Posts: 71
Answering my own dumb question after some research, 1 ton=12,000 btuh, so my 4-ton system looks good for the main floor calculation ~45,000. I'm surprise my upstairs heat calculation was 45,000 also but A/C was only 15,000. Don't know what that means for my 2-ton system.
There's no urgency to replace my system, since it's working, but I will have to try to figure out the payback period of a new system to see if it makes sense to upgrade even though the current system is still operational.
ExitLeft is offline   Reply With Quote
Old 08-11-2017, 05:19 PM   #25
Full time employment: Posting here.
 
Join Date: Jun 2012
Posts: 691
This looks like a Manual J calc

Quote:
Originally Posted by ExitLeft View Post
I don't know anything about Manual J. I'm just a DIY homeowner. But I found this site to help me calculate it: coolcalc.com (free online system, uses GPS to simplify measurements; but requires signup.)
I've attached the calculated output for my 2 systems and would like help understanding what it means
FYI, my home was built in 1999, has 2 levels (~4k sqft)+finished basement, York Diamond 80 (4 ton) for 1st level/bsmt (split zone) and York Diamond 80 (2 ton) for upstairs. LP heat + single stage A/C in both.
The systems are old, but still in good working order. I've done some repairs (capacitors, 1 blower and 1 main board). My neighbor recently priced 2-stage replacements (similar home/same Yorks) at $15,500 for both systems (Bryant 4-ton, 16 seer and 3-ton 17 seer). I asked their contractor if he did Manual J for them, but no response yet.
TIA!
someguy is offline   Reply With Quote
Old 08-11-2017, 06:44 PM   #26
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
target2019's Avatar
 
Join Date: Dec 2008
Location: On a hill in the Pine Barrens
Posts: 9,722
Quote:
Originally Posted by ExitLeft View Post
Answering my own dumb question after some research, 1 ton=12,000 btuh, so my 4-ton system looks good for the main floor calculation ~45,000. I'm surprise my upstairs heat calculation was 45,000 also but A/C was only 15,000. Don't know what that means for my 2-ton system.
There's no urgency to replace my system, since it's working, but I will have to try to figure out the payback period of a new system to see if it makes sense to upgrade even though the current system is still operational.
The 2 ton A/C rating is not used for heat. The furnace will have another rating. For example, my A/C is 2.5 ton, but the furnace is 80,000 BTU.
target2019 is online now   Reply With Quote
Old 08-11-2017, 07:05 PM   #27
Full time employment: Posting here.
 
Join Date: Nov 2008
Location: Louisville
Posts: 601
When we bought our current house, the home inspector said he thought the AC was too small. I called an HVAC company to do an inspection. They said our AC was too small. I contacted the owner with the concerns. He was a nuclear engineer and sized the system himself. I reviewed his numbers. We bought the house.

Every few months the local utility sends us a letter informing us the utility cost for our home is lower than any other house around. The previous owner was right.

If you read the HVAC forums, there is a big difference between what the HVAC engineers say to do, and what the local dealers actually do. The reasoning is that if you oversize the AC system, you never get a call back from the customer with a complaint. But the systems work better if they run for a longer time. They dehumidify the house better and are smaller and more efficient.
Masquernom is offline   Reply With Quote
Old 08-11-2017, 07:34 PM   #28
Recycles dryer sheets
 
Join Date: Mar 2014
Location: Annapolis
Posts: 71
Quote:
Originally Posted by Masquernom View Post
But the systems work better if they run for a longer time. They dehumidify the house better and are smaller and more efficient.
This isn't true for single-stage systems, though, right? Or if it is true, should I leave the fan in the "on" position, rather than auto? I don't see how that would save energy though, unless it results in the A/C rarely running as a result.

I went so far as putting in my own manual baffles in the ducts for our upstairs systems, so that I could turn off the kids' rooms when they were away at college, etc. (keeping their doors closed as well). I wonder if that saves energy or just screws up the "balance" of the system?
ExitLeft is offline   Reply With Quote
Old 08-11-2017, 07:53 PM   #29
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
Quote:
Originally Posted by ExitLeft View Post
I'm surprise my upstairs heat calculation was 45,000 also but A/C was only 15,000. Don't know what that means for my 2-ton system.
You may want to check to be sure about your design temp for the summer at your location. I couldn't find Thomas Point listed in the tables I found, but there was >nowhere< in Maryland with a 1% design cooling temperature as low as the 85 deg F you used. Baltimore is 91 deg F, and the "coolest" summertime town I found in MD had a design temp of 88 deg F. Here's the EPA table.
samclem is offline   Reply With Quote
Old 08-11-2017, 07:54 PM   #30
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 14,328
Quote:
Originally Posted by ExitLeft View Post
This isn't true for single-stage systems, though, right? Or if it is true, should I leave the fan in the "on" position, rather than auto? I don't see how that would save energy though, unless it results in the A/C rarely running as a result..........
The fan control only runs the fan. What dehumidifies is running the interior air over the cold coil in the air handler / furnace. If the compressor is not running, the coil doesn't stay cold for long. So, a smaller compressor allows more run time in the cold coil condition.
travelover is offline   Reply With Quote
Old 08-11-2017, 09:19 PM   #31
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,242
Quote:
Originally Posted by Masquernom View Post
When we bought our current house, the home inspector said he thought the AC was too small. I called an HVAC company to do an inspection. They said our AC was too small. I contacted the owner with the concerns. He was a nuclear engineer and sized the system himself. I reviewed his numbers. We bought the house.

Every few months the local utility sends us a letter informing us the utility cost for our home is lower than any other house around. The previous owner was right.

If you read the HVAC forums, there is a big difference between what the HVAC engineers say to do, and what the local dealers actually do. The reasoning is that if you oversize the AC system, you never get a call back from the customer with a complaint. But the systems work better if they run for a longer time. They dehumidify the house better and are smaller and more efficient.

Not always.... my friend is having my AC guy come by because the last person oversized his and it cycles way too much... he said he has put up with it for 10 years and finally has gotten so frustrated he is going to do something about it...
Texas Proud is offline   Reply With Quote
Old 08-12-2017, 06:55 PM   #32
Recycles dryer sheets
 
Join Date: Mar 2014
Location: Annapolis
Posts: 71
Quote:
Originally Posted by samclem View Post
You may want to check to be sure about your design temp for the summer at your location. I couldn't find Thomas Point listed in the tables I found, but there was >nowhere< in Maryland with a 1% design cooling temperature as low as the 85 deg F you used. Baltimore is 91 deg F, and the "coolest" summertime town I found in MD had a design temp of 88 deg F. Here's the EPA table.
Thanks for that info. We are in Anne Arundel County, 91 deg F. The 'coolcalc' website pulled that Thomas Point data based on their GPS info.
ExitLeft is offline   Reply With Quote
Old 08-12-2017, 07:03 PM   #33
Recycles dryer sheets
 
Join Date: Mar 2014
Location: Annapolis
Posts: 71
Quote:
Originally Posted by travelover View Post
The fan control only runs the fan. What dehumidifies is running the interior air over the cold coil in the air handler / furnace. If the compressor is not running, the coil doesn't stay cold for long. So, a smaller compressor allows more run time in the cold coil condition.
Is it the constant dehumidifying that results in the lower electric bill? I just want to reduce my electricity consumption. According to utility, we use 56% more electric than the top 20% "most efficient" neighbors, but use 5% less than "all neighbors." Doesn't make me feel good when I have a $280 bill to pay this month...

I should note that we keep the main living area set to 77 deg and the upstairs at 85 until evening and then upstairs drops to 74 and main living gets turned off. Always have left the fan in "auto" position. In the winter, we use about 1,300 kwh/month and peak summer goes up to 2,300, I assume 90%+ driven by the A/C usage.
ExitLeft is offline   Reply With Quote
Old 08-12-2017, 07:12 PM   #34
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 26,895
Quote:
Originally Posted by ExitLeft View Post
Is it the constant dehumidifying that results in the lower electric bill? I just want to reduce my electricity consumption. According to utility, we use 56% more electric than the top 20% "most efficient" neighbors, but use 5% less than "all neighbors." Doesn't make me feel good when I have a $280 bill to pay this month...

I should note that we keep the main living area set to 77 deg and the upstairs at 85 until evening and then upstairs drops to 74 and main living gets turned off. Always have left the fan in "auto" position.
It really depends on your circumstances. There is no general answer.

Someone in Phoenix isn't dealing with humidity, but they are dealing with heat.

In my case, we really can't have much in the way of shade trees, and the west Sun just beats on our house, two stories with a basement (so 2 stories getting hit by the sun. But my Mom's house, in the same climate, had a lot of old oak shade, a ranch with full basement, so LOTs of humidity coming up from that basement. I think their unit was over-sized (don't know the rating), and I'd go there and it would be like 67 F, and clammy. She had to keep turning down the thermostat in an attempt to get the humidity lowered. And had a de-humidifier running in the basement.

You want long cycles for efficiency and humidity removal, and that means a smaller unit. But on a really hot summer day, with sun hitting the house, and people over, you need a large unit. That's why I went for the 2-stage and variable speed fan. But not everyone needs that.

It depends.

-ERD50
ERD50 is offline   Reply With Quote
Old 08-12-2017, 07:20 PM   #35
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
samclem's Avatar
 
Join Date: May 2004
Location: SW Ohio
Posts: 14,404
Quote:
Originally Posted by ExitLeft View Post
Is it the constant dehumidifying that results in the lower electric bill? I just want to reduce my electricity consumption.
If we take two identical homes and one has a "too big" AC unit and the other has a "correct size AC unit, and both homes set the thermostat to the same temperature, then the home with the "too big" AC unit will have higher indoor humidity. And that will be less comfortable, likely prompting the owner to set the temperature lower (in order to get the same "wet bulb" indoor temperature, which is what really determines the comfort to occupants). And setting the temperature lower will increase electricity costs. So, indirectly, a smaller AC unit will generally reduce operating costs.
samclem is offline   Reply With Quote
Old 08-12-2017, 07:31 PM   #36
Recycles dryer sheets
 
Join Date: Mar 2014
Location: Annapolis
Posts: 71
Quote:
Originally Posted by samclem View Post
If we take two identical homes and one has a "too big" AC unit and the other has a "correct size AC unit, and both homes set the thermostat to the same temperature, then the home with the "too big" AC unit will have higher indoor humidity. And that will be less comfortable, likely prompting the owner to set the temperature lower (in order to get the same "wet bulb" indoor temperature, which is what really determines the comfort to occupants). And setting the temperature lower will increase electricity costs. So, indirectly, a smaller AC unit will generally reduce operating costs.
Ah, brilliant. We have extreme humidity in Maryland. I guess I need to do some hard math comparing how long my A/C runs per day*kw used vs assumptions of a 2-stage or variable in lowest electric mode running over a longer period set at a couple degrees higher (assuming higher temp could be comfortable with lower humidity) to figure out the potential electric cost difference.
ExitLeft is offline   Reply With Quote
Old 08-12-2017, 08:12 PM   #37
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,242
Quote:
Originally Posted by samclem View Post
If we take two identical homes and one has a "too big" AC unit and the other has a "correct size AC unit, and both homes set the thermostat to the same temperature, then the home with the "too big" AC unit will have higher indoor humidity. And that will be less comfortable, likely prompting the owner to set the temperature lower (in order to get the same "wet bulb" indoor temperature, which is what really determines the comfort to occupants). And setting the temperature lower will increase electricity costs. So, indirectly, a smaller AC unit will generally reduce operating costs.
I have no idea if this is true, but our AC guy said that the start up of an AC system takes a lot of electricity..... so in your example even if they did not turn the temp down, the larger unit would cycle many more times and also use up more electricity...


I checked my unit for yesterday.... it ran 77% of the day... most of the time I looked it was in the 30% range for the compressor with some times going as high as 70%...

Have not had it long enough to know if less electricity... but it does seem a bit more comfortable... not as good as they were making it out, but more even...

BTW, I have mine set to 45% humidity, but it struggles to get below 50%... one of the techs who came out to move a sensor said that it is almost impossible to get lower on an 'old' house (built in late 70s or early 80s)... the newer houses are tighter and easier to get moisture out...
Texas Proud is offline   Reply With Quote
Old 08-12-2017, 09:35 PM   #38
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 26,895
Quote:
Originally Posted by Texas Proud View Post
I have no idea if this is true, but our AC guy said that the start up of an AC system takes a lot of electricity.....
I think that gets exaggerated a bit (but not 'wrong'). Yes, start up currents are high for a motor (maybe not so much for variable speed motors though?), but that's only a few seconds. If it were much higher for much longer, your circuit breaker would pop.

Quote:
so in your example even if they did not turn the temp down, the larger unit would cycle many more times and also use up more electricity...
But yes, cycling often does lower efficiency - it takes time to circulate the 'cool'.


Quote:
I checked my unit for yesterday.... it ran 77% of the day... most of the time I looked it was in the 30% range for the compressor with some times going as high as 70%...

Have not had it long enough to know if less electricity... but it does seem a bit more comfortable... not as good as they were making it out, but more even...

BTW, I have mine set to 45% humidity, but it struggles to get below 50%... one of the techs who came out to move a sensor said that it is almost impossible to get lower on an 'old' house (built in late 70s or early 80s)... the newer houses are tighter and easier to get moisture out...
That sounds pretty reasonable to me. Running that long and that low indicates it is working to get the humidity down. The bumps up to 70% are probably the peaks of the summer sun, or when running that long just isn't quite keeping up.

The worst of the heat/humidity we get here in N IL is probably similar to what you experience on a 'bad' (but not excessively bad) day in Texas. I think our is set for 45% humidity, and low 50's seems to be what we can expect. Even though I hate the heat/humidity, I find that by the time the inside is low 50's in RH and 77F or lower, we are comfortable. Seems to be a big difference between that and ~ 65 RH inside (it might be 70's/80's/90's RH outside, with temps in the 90's).

Ahhh, one more thing I noticed. These smart thermostats are pretty flexible. The old ones, you got a temperature and a range (say set to 76F, it maintains 75-77, turning on/off at those points). Another way they work to keep the humidity controlled, and keep the cycles so they are not too short or too long, is they will make that range wider or tighter dynamically. I found a setting in the thermostats called CPH (cycles per hour). It was set to 5, I set it to 4. Meaning that at "4" it will try (within other limits/conditions) to be on for 7.5 minutes, off for 7.5 minutes, so 4 cycles per hour. So if it's hot out, it might tighten that range a bit. If it's cool out, it widens the range to keep the A/C running a little longer. I wish I understood all the algorithms, but it seems to work well.

-ERD50
ERD50 is offline   Reply With Quote
Old 08-13-2017, 07:20 AM   #39
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
target2019's Avatar
 
Join Date: Dec 2008
Location: On a hill in the Pine Barrens
Posts: 9,722
Quote:
Originally Posted by ExitLeft View Post
Is it the constant dehumidifying that results in the lower electric bill? I just want to reduce my electricity consumption. According to utility, we use 56% more electric than the top 20% "most efficient" neighbors, but use 5% less than "all neighbors." Doesn't make me feel good when I have a $280 bill to pay this month...

I should note that we keep the main living area set to 77 deg and the upstairs at 85 until evening and then upstairs drops to 74 and main living gets turned off. Always have left the fan in "auto" position. In the winter, we use about 1,300 kwh/month and peak summer goes up to 2,300, I assume 90%+ driven by the A/C usage.
It's a combination of things. I think your d/s unit is oversized, and u/s is possibly undersized. Is the house well-insulated? High celings? How about the distribution system?

My 1975 house is 3000SF on 2 floors. Can't really fix the original design, but high ceilings and features like cathedral ceiling mean significantly more space to fill with heat, and dehumidify.

Replace all windows when moved in. Attic insulation made an incredible difference. Replace large sliders and entrance door. Replaced both 40-year old systems.

Finally, last year we reached comfort. And gas/electric bills are down 25% or more.

Note: if you lower upstairs system under 80 in the summer, downstairs might work less, and be more comfortable.
target2019 is online now   Reply With Quote
Old 08-13-2017, 07:32 AM   #40
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
target2019's Avatar
 
Join Date: Dec 2008
Location: On a hill in the Pine Barrens
Posts: 9,722
Quote:
Originally Posted by ExitLeft View Post
Ah, brilliant. We have extreme humidity in Maryland. I guess I need to do some hard math comparing how long my A/C runs per day*kw used vs assumptions of a 2-stage or variable in lowest electric mode running over a longer period set at a couple degrees higher (assuming higher temp could be comfortable with lower humidity) to figure out the potential electric cost difference.
Your humidity problem is worse than ours, in South NJ. When I bought these VS systems, I recall the contractor mentioned I would not benefit from two-stage. However, if I was near the ocean, he would recommend it.

One thing I can do with these VS systems, is run the fans continuously at a very low speed. This helps early and late in the seasons, before heating or A/C is required to be on.
target2019 is online now   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
The HVAC Saga Continues redduck Other topics 8 09-18-2016 09:01 PM
Shopping HVAC - Upstairs rpguy4 Other topics 7 12-31-2015 01:20 PM
HVAC replacement question Texas Proud Other topics 99 10-14-2014 05:29 PM
HVAC Replacement: Reality, or Rip-off? Amethyst Other topics 35 04-21-2014 08:01 PM