I had the A/C unit replaced this summer. Now that its heat season, I had air blowing but no heat and called the installer to come look at it. I'm now skeptical of what I'm being told and need some advice.

I have a 2 zone, 1 stage system with a hybrid heat pump valve on the A/C unit and a gas furnace as alternate. The repairman that came mentioned that the reversing valve had been left wired for straight cooling only. That made me wonder later if that error had been deliberate to require a heat related repair. Trying to set it up correctly, he concludes the zone panel (Honeywell mini-zone) is not sending current to the heat pump reversing valve and needs to be replaced to the tune of $2800. My "inner cheap" was alarmed by that price. The other functions of the board were working. An alternative to replacing the panel would be to just not use the heat pump valve and go to a straight heat/ac setup. He said changing the wiring would take at least a half a day and cost $489. That also sounded wrong to me because originally changing over the wiring for the hybrid valve only took the original installer an hour or so.

I looked for similar zone panels online and found what I think is a similar Honeywell panel for the setup I have (Honeywell HZ322) and suppliers sell them online in the low $200s, but I don't really know anything about HVAC and wouldn't attempt to do it myself.

Questions:
  1. Is $2800 a ripoff or reasonable price for replacing a zone panel for a 1 stage, 2 zone hyrid heat pump system?
  2. Running the heat pump hybrid is supposed to save money, but I have a 90% gas furnace and reasonable gas rates in a Knoxville Tennessee climate. Depending upon the cost of a zone panel, could wiring to exclude the heat pump make sense or is that a shortsighted short term fix that I should avoid because the rest of the zone panel will die at some point anyway (it was probably installed in 2005)?
I plan to get another estimate, but could use any advice you have concerning reasonable costs and on whether to replace the zone panel. Am I just just not informed on costs or is my "inner cheap" correct to be alarmed by the prices quoted? The repairman left the system with the reversing valve on heat only, so I do have heat but no A/C until I do something.

Thanks.
gromit is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 10-16-2018, 11:54 AM   #2
Moderator
braumeister's Avatar
 
Join Date: Feb 2010
Location: Flyover country
Posts: 25,362
At those dollar amounts I would get at least three quotes from different companies.
__________________
I thought growing old would take longer.
braumeister is offline   Reply With Quote
Old 10-16-2018, 11:57 AM   #3
Thinks s/he gets paid by the post
 
Join Date: Jun 2016
Posts: 1,961
Call the company that originally installed the new system.
Just because the new guy says the original installer disabled the heat pump does not mean he is the one telling the truth... especially since he wants to charge $2800 to fix it.


If the original company doesn't backup the install, go to the manufacturer to report a bad dealer and see if the manufacturer warranty will be honored by another dealer.
Spock is offline   Reply With Quote
Old 10-16-2018, 11:59 AM   #4
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 14,328
I'd definitely get a second opinion and you might get help on this HVAC forum.They are mostly HVAC techs and won't help you fix it yourself, but will give opinions on how a tech should fix it.

My gut feeling is that if the AC was just installed and it has heat pump capabilities, all of that functionality should have been tested and in working order.
travelover is offline   Reply With Quote
Old 10-16-2018, 12:14 PM   #5
Recycles dryer sheets
gromit's Avatar
 
Join Date: May 2010
Location: Knoxville
Posts: 369
Quote:
Originally Posted by Spock View Post
Call the company that originally installed the new system.
Just because the new guy says the original installer disabled the heat pump does not mean he is the one telling the truth... especially since he wants to charge $2800 to fix it.


If the original company doesn't backup the install, go to the manufacturer to report a bad dealer and see if the manufacturer warranty will be honored by another dealer.

Just to clarify - the repairman is a different person, but the same company as the original installer.
gromit is offline   Reply With Quote
Old 10-16-2018, 12:21 PM   #6
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 14,328
Quote:
Originally Posted by gromit View Post
Just to clarify - the repairman is a different person, but the same company as the original installer.
He may not know what he is talking about - you need to get back to the owner / manager and find out why it wasn't done right.
travelover is offline   Reply With Quote
Old 10-16-2018, 12:23 PM   #7
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
Big_Hitter's Avatar
 
Join Date: May 2013
Location: Les Bois
Posts: 5,761
15 years or so ago I got a quote for $500 to replace a circuit board in one of our furnaces - the part cost $100

I got mad and bought the part and put it in myself, it was really easy. I just took a photo of it before i pulled all the wires off and put them all back on the same way, screwed the board back in and returned power. I never used the company again.

Not sure what yours would take I'd suggest going to a HVAC repair forum and ask your question there.
__________________
You can't be a retirement plan actuary without a retirement plan, otherwise you lose all credibility...
Big_Hitter is offline   Reply With Quote
Old 10-16-2018, 12:24 PM   #8
Thinks s/he gets paid by the post
 
Join Date: Jun 2016
Posts: 1,961
Quote:
Originally Posted by gromit View Post
JUst to clarify - the repairman is a different person, but the same company as the original installer.
Dad put in 6K worth of new AC in 2017 (desert SW, 105-110 degree outdoor temps).
Middle of this 2018 summer the house started running a little warm and the AC was running a lot.
Tech from the installing company said it was just the thermostat reading the wrong temp.

Dad bought thermometer and found it was reading the same.
Called the company back and they sent out another tech who found one of the ducts under the floor had come partially disconnected. The cool air was being blown into the crawl space with a little getting into the house.

Still call the original installer... if the wiring was done wrong they should still fix it and not charge $2800. If they bulk, start calling the manufacturer.
Spock is offline   Reply With Quote
Old 10-16-2018, 12:25 PM   #9
Thinks s/he gets paid by the post
nash031's Avatar
 
Join Date: Jun 2013
Location: Bonita (San Diego)
Posts: 1,795
Quote:
Originally Posted by Big_Hitter View Post
15 years or so ago I got a quote for $500 to replace a circuit board in one of our furnaces - the part cost $100

I got mad and bought the part and put it in myself, it was really easy. I just took a photo of it before i pulled all the wires off and put them all back on the same way, screwed the board back in and returned power. I never used the company again.

Not sure what yours would take I'd suggest going to a HVAC repair forum and ask your question there.
And that was before the advent of YouTube. YouTube - "Helping Average Joes Screw Up Home Maintenance Projects since 2005".
__________________
"So we beat to our own drummer in the sun;
We ask for nobody's permission to run.
I just wanna live in a world like that;
Now I'm gonna live in a world like that!" - World Like That, O.A.R.
nash031 is offline   Reply With Quote
Old 10-16-2018, 12:26 PM   #10
Moderator Emeritus
aja8888's Avatar
 
Join Date: Apr 2011
Location: Conroe, Texas
Posts: 18,735
Any "deliberate" wiring change from normal operation should have been brought to your attention at the time of install. Something sounds "fishy".
__________________
*********Go Yankees!*********
aja8888 is offline   Reply With Quote
Old 10-16-2018, 12:42 PM   #11
Recycles dryer sheets
gromit's Avatar
 
Join Date: May 2010
Location: Knoxville
Posts: 369
Quote:
Originally Posted by travelover View Post
He may not know what he is talking about - you need to get back to the owner / manager and find out why it wasn't done right.
Thanks. I agree on both points. Because I have heat, I'm going to take a few days to get myself organized. Before I talk to the owner, I'm soaking in the advice here and then I want to get another estimate for a zone panel installation just so I have an idea of whether or not they're in the ballpark of fair prices.
gromit is offline   Reply With Quote
Old 10-16-2018, 12:49 PM   #12
Recycles dryer sheets
gromit's Avatar
 
Join Date: May 2010
Location: Knoxville
Posts: 369
Quote:
Originally Posted by aja8888 View Post
Any "deliberate" wiring change from normal operation should have been brought to your attention at the time of install. Something sounds "fishy".
I agree if they weren't going to leave the heat pump valve wired correctly I should've been told. I watched the entire original installation.
gromit is offline   Reply With Quote
Old 10-16-2018, 12:52 PM   #13
Thinks s/he gets paid by the post
 
Join Date: Nov 2011
Posts: 3,906
$2800 sounds way high for what you describe. Those type components can usually be had new for $100 to $500.
GrayHare is offline   Reply With Quote
Old 10-16-2018, 12:58 PM   #14
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
Big_Hitter's Avatar
 
Join Date: May 2013
Location: Les Bois
Posts: 5,761
Quote:
Originally Posted by GrayHare View Post
$2800 sounds way high for what you describe. Those type components can usually be had new for $100 to $500.
and the installation looks straight-forward too

https://www.supplyhouse.com/Honeywel...iABEgIo_vD_BwE
__________________
You can't be a retirement plan actuary without a retirement plan, otherwise you lose all credibility...
Big_Hitter is offline   Reply With Quote
Old 10-16-2018, 01:14 PM   #15
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2005
Posts: 17,244
Quote:
Originally Posted by Spock View Post
Call the company that originally installed the new system.
Just because the new guy says the original installer disabled the heat pump does not mean he is the one telling the truth... especially since he wants to charge $2800 to fix it.


If the original company doesn't backup the install, go to the manufacturer to report a bad dealer and see if the manufacturer warranty will be honored by another dealer.

+1 on this!!!! It is the job of the original installer to install properly... if the heat is not working then they did not install properly... they should come out and get it right for FREE...


My question is why did you call a different company? And if you called the same then you need to talk to the owner about that tech or how they are cheating you... make sure you put in a bad review IF they do not get it fixed for free...
Texas Proud is offline   Reply With Quote
Old 10-16-2018, 01:26 PM   #16
Recycles dryer sheets
gromit's Avatar
 
Join Date: May 2010
Location: Knoxville
Posts: 369
Quote:
Originally Posted by Texas Proud View Post
+1 on this!!!! It is the job of the original installer to install properly... if the heat is not working then they did not install properly... they should come out and get it right for FREE...


My question is why did you call a different company? And if you called the same then you need to talk to the owner about that tech or how they are cheating you... make sure you put in a bad review IF they do not get it fixed for free...
I called the same company. I agree they should've left me with working heat, which I had before they started. Had they done their job they might have discovered an already bad zone panel. Is the zone panel really bad? I can only guess yes because of the time the tech spent trying to diagnose it, but its possible the tech is dishonest and/or incompetent. I argued with the tech that if I chose to have them wire it back like it was ORIGINALLY, before they changed it, ie without the heat pump valve, that should be a part of the A/C installation at no expense to me. He disagreed and I was clear to him that I planned to talk to the owner about it.

One thing I need to resolve first is what do I want. Do I want to replace the board to use the heat pump, at some expense, probably by another company, or do I want to just not use the heat pump and fight with the original company over whether changing the wiring should be at their expense.
Thanks for the input.
gromit is offline   Reply With Quote
Old 10-16-2018, 01:32 PM   #17
Thinks s/he gets paid by the post
Lakewood90712's Avatar
 
Join Date: Jul 2005
Posts: 2,223
Quote:
Originally Posted by gromit View Post
Just to clarify - the repairman is a different person, but the same company as the original installer.
Time to have a chat with the company owner at your house.

FWIW , If you have good gas rates, skip the heat pump setup IMO, and leave the reversing valve disconnected. You will save a lot of grief in the long run. Just my 2 cents worth. Feel free to PM me on this if you want a very long winded opinion.
Lakewood90712 is offline   Reply With Quote
Old 10-16-2018, 02:55 PM   #18
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 14,328
Quote:
Originally Posted by Lakewood90712 View Post
............FWIW , If you have good gas rates, skip the heat pump setup IMO, and leave the reversing valve disconnected. You will save a lot of grief in the long run...........
But if natural gas is inexpensive, why install a heat pump as opposed to an AC unit, at all?
travelover is offline   Reply With Quote
Old 10-16-2018, 03:11 PM   #19
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
JoeWras's Avatar
 
Join Date: Sep 2012
Posts: 11,702
Quote:
Originally Posted by travelover View Post
But if natural gas is inexpensive, why install a heat pump as opposed to an AC unit, at all?
gromit will have to reply for their exact situation, but I can speak for the south in general.

There is (was) a lot of push for all electric homes in the south, especially 30 odd years ago. Many homes don't even have gas service.

This is changing, especially in light of the preference for gas cooking.

Anyway, call it a bias.

Personally, we have gas service and gas heat and water. However, when I had a second unit installed for upstairs, I opted for a heat pump to avoid running gas in the attic. The main downstairs heat takes most of the load to the upstairs anyway, so this actually works well, with very little need for auxiliary heat. I'm still very glad to have gas heat downstairs.

To babble a little further: many people these days are opting for the mini-split systems in our area for such upstairs or bonus room retro-fits. Some of them are pretty slick.
JoeWras is offline   Reply With Quote
Old 10-16-2018, 03:30 PM   #20
Recycles dryer sheets
gromit's Avatar
 
Join Date: May 2010
Location: Knoxville
Posts: 369
Quote:
Originally Posted by travelover View Post
But if natural gas is inexpensive, why install a heat pump as opposed to an AC unit, at all?
I replaced the A/C during a heatwave. The installers ordered it from the supplier, and when they went to pick it up the supplier realized they didn't have it. The supplier decided to give them the next step up unit, 1 higher seer, that included a heat pump reversing valve for no extra charge. So the heat pump wasn't ordered, I just ended up with having it available on the unit.
gromit is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Heat Pump Recommendations, Trane and Other John Galt III Other topics 15 01-23-2018 11:25 AM
Split AC system with heat pump Bimmerbill Other topics 12 05-29-2014 05:09 PM
Heat pump in HUMID Houston? Sam Other topics 16 01-05-2010 10:02 AM
Geothermal Heat Pump jazz4cash Other topics 36 03-13-2008 01:08 PM

» Quick Links

 
All times are GMT -6. The time now is 12:43 AM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.