A/C not blowing cold.....

Went out to the lakehouse today and turned on the A/C. Noticed after about 10 minutes that it wasn't blowing cold - it has been working great every weekend up until today.

Checked the compressor outside (Rheem 4 ton 14 SEER). The compressor was running (hot to touch), condensor fan was running and blowing cold air, both low and high side tubing felt ambient to touch.

Same thing happened a couple of years ago when the expansion valve was blamed and replaced.

I've called the same service company to come out and take a look at it this week, am wondering if there are any A/C people here who might have an opinion?
__________________

__________________
LakeTravis is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 04-28-2013, 07:45 PM   #2
Moderator Emeritus
 
Join Date: May 2007
Posts: 11,038
Low refrigerant pressure due to a leak maybe?
__________________

__________________
FIREd is online now   Reply With Quote
Old 04-28-2013, 08:10 PM   #3
Thinks s/he gets paid by the post
frayne's Avatar
 
Join Date: Oct 2002
Location: 19th Hole
Posts: 2,529
Quote:
Originally Posted by FIREd View Post
Low refrigerant pressure due to a leak maybe?

My thoughts as well.
__________________
A totally unblemished life is only for saints.
frayne is offline   Reply With Quote
Old 04-28-2013, 08:59 PM   #4
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
RunningBum's Avatar
 
Join Date: Jun 2007
Posts: 5,176
Back when I lived in the Austin area, I heard stories of kids huffing freon. They'd get high, you'd get warm.
__________________
RunningBum is offline   Reply With Quote
Old 04-28-2013, 09:07 PM   #5
Thinks s/he gets paid by the post
gauss's Avatar
 
Join Date: Aug 2011
Posts: 1,708
Was the compressor actually running, or was it just buzzing?

I have had problems where the start-run capacitor went bad and the compressor would not start but just buzz.

One way to confirm that the capacitor is in good order is to:

#1) remove power to ac unit

#2) put a DC voltmeter across all the capacitor terminals to determine if there is any remaining charge in the capacitor.


#3) if significant charge still exists (ie > 20 Vdc) in the cap, discharge it either with a screwdriver blade or more properly with a set of aligator clips with a 1k resistor in series. Observe the charge bleed off by watching the meter.

#4) Once the capacitor is out of the circuit and complete discharged, place the multimeter into resistance mode on the highest resistance setting (ie 2 MOhm)

#5) A properly functioning capacitor will start at 0 ohms resistance and increase up to a very large/infinite value over time.

If you think that your capacitor is bad, Grainger stocks common replacement caps for reasonable costs -- the only problem is that you need to make purchases on a business account (I always referenced my MegaCorp's account together with a cash purchase).

Note I am not an A/C professional, but rather an frugal guy who likes to repair his own stuff. The above description may not be complete or totally correct. You are responsible to verify any information given to protect your hardware and your own safety.

-gauss
__________________
gauss is offline   Reply With Quote
Old 04-28-2013, 09:21 PM   #6
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: May 2004
Posts: 11,615
Just to check: You say "the condenser fan was running and blowing cold air". The condenser fan (the one outside) should have been blowing hot air out of the unit. That outside fan was running okay when the compressor was running, right?
__________________
"Freedom begins when you tell Mrs. Grundy to go fly a kite." - R. Heinlein
samclem is offline   Reply With Quote
Old 04-29-2013, 06:30 AM   #7
gone traveling
 
Join Date: Jun 2012
Location: Austin
Posts: 245
Yes, the outside unit was blowing cold air as opposed to the hot air it should have been blowing if it was properly removing the heat from the condensor coils.

The capacitor is good, both the condensor fan and the compressor are running although the compressor was getting hot to the touch - I didn't let it run long enough to tell if the low-pressure cut off would have shut down the compressor before it was damaged, nor did I remove the caps on both of the freon lines and push in on the valves to see if there was actually freon in the lines.

I'm a bit hesitant to think that it suddenly lost all freon since the weekend before it worked fine - but I suppose that is possible.

More likely the expansion valve they replaced a couple of years ago is stuck and not allowing freon to flow to the condensor. Curious to see what they tell me when they have a chance to check it out.
__________________
LakeTravis is offline   Reply With Quote
Old 04-29-2013, 07:29 AM   #8
Thinks s/he gets paid by the post
 
Join Date: Jul 2012
Location: Mississippi
Posts: 1,878
Quote:
Originally Posted by LakeTravis View Post
I'm a bit hesitant to think that it suddenly lost all freon since the weekend before it worked fine - but I suppose that is possible.
That is exactly what happened to mine. Small pin hole leak in compressor. Working one day, nothing the next. It would not stay charged when they filled it. They had a "sniffer" and detected where the leak was at.
__________________
rbmrtn is offline   Reply With Quote
Old 04-29-2013, 08:31 AM   #9
gone traveling
 
Join Date: Jul 2007
Posts: 333
Quote:
Originally Posted by rbmrtn View Post
That is exactly what happened to mine. Small pin hole leak in compressor. Working one day, nothing the next. It would not stay charged when they filled it. They had a "sniffer" and detected where the leak was at.
Same thing happend to one of my AC unit's a few years ago.
__________________
HighRoller is offline   Reply With Quote
Old 04-29-2013, 11:45 AM   #10
Moderator Emeritus
 
Join Date: May 2007
Posts: 11,038
Quote:
Originally Posted by LakeTravis View Post
I'm a bit hesitant to think that it suddenly lost all freon since the weekend before it worked fine - but I suppose that is possible.
It could be a slow leak and once the pressure falls below a critical threshold, the system suddenly stops working properly. That's exactly what happened to my old A/C unit. It had a very small leak in the condenser and it would take about a year for the pressure to drop below the threshold. But when it did, the system would stop working all of the sudden.
__________________
FIREd is online now   Reply With Quote
Old 04-29-2013, 12:28 PM   #11
Thinks s/he gets paid by the post
 
Join Date: Jun 2004
Location: E. Wash
Posts: 1,057
We have a similar situation when we change over from heat to cool. Apparently there is a switch that regulates but it does not always reset. Tech manually reset on his service call. However, he told me I could do the same thing by simply flipping the power off and letting the system reboot when power is restored.
May not work but can not beat the cost.
Nwsteve
__________________
nwsteve is offline   Reply With Quote
Old 04-29-2013, 03:27 PM   #12
gone traveling
 
Join Date: Jun 2012
Location: Austin
Posts: 245
Well, it turns out that it IS a leak - the condensor coil in the outside unit is leaking.

It's a 4 ton, 12 SEER R-22 Rheem unit and they haven't confirmed yet but they are thinking it will be around $3K to replace it - and almost a full third of that is for R-22 refrigerant which is roughly $70 a pound.

There is a slight possibility the unit is still under warranty, it will be 10 years old in 3 months and Rheem has a 10 year parts warranty IF the unit was registered within 2 months of installation, otherwise the warranty period is only 5 years.

I can't remember if we registered the A/C unit after we closed on this new house in July 2003, but......I'm obviously hoping we did...
__________________
LakeTravis is offline   Reply With Quote
Old 04-29-2013, 04:01 PM   #13
Full time employment: Posting here.
sailor's Avatar
 
Join Date: May 2005
Location: Atlanta suburbs
Posts: 881
Quote:
Originally Posted by LakeTravis View Post
It's a 4 ton, 12 SEER R-22 Rheem unit and they haven't confirmed yet but they are thinking it will be around $3K to replace it - and almost a full third of that is for R-22 refrigerant which is roughly $70 a pound.
Wow, that's a good markup for your HVAC tech.
30 lbs jugs of R-22 go for about $450 locally.
Your 4 ton unit total charge should be maybe 15 lbs.
__________________
sailor is offline   Reply With Quote
Old 04-29-2013, 04:20 PM   #14
gone traveling
 
Join Date: Jun 2012
Location: Austin
Posts: 245
Quote:
Originally Posted by sailor View Post
Wow, that's a good markup for your HVAC tech.
30 lbs jugs of R-22 go for about $450 locally.
Your 4 ton unit total charge should be maybe 15 lbs.
Wow, you're not kidding - I did a few searches on Austin Craigslist and came up with plenty of R-22 for way less than $70 a pound. Going to have to ask them why they are so high, calls everything else they quote into suspicion. Disappointed to see that, I've used this outfit several times over the last decade as they are right down the street from this property and their pricing was always fair.
__________________
LakeTravis is offline   Reply With Quote
Old 04-29-2013, 04:33 PM   #15
Thinks s/he gets paid by the post
gauss's Avatar
 
Join Date: Aug 2011
Posts: 1,708
When I worked on the capacitor problem that I described above, this was after the HVAC techs called it a bad compressor and wanted to sell us a whole new outside unit.

I suspect many of the HVAC techs would rather have you pay them to install a new unit as opposed to repair an old unit due to the higher likelikhood of callbacks on the repaired unit.

-gauss
__________________
gauss is offline   Reply With Quote
Old 04-29-2013, 04:49 PM   #16
Moderator Emeritus
 
Join Date: May 2007
Posts: 11,038
Quote:
Originally Posted by LakeTravis View Post

It's a 4 ton, 12 SEER R-22 Rheem unit and they haven't confirmed yet but they are thinking it will be around $3K to replace it - and almost a full third of that is for R-22 refrigerant which is roughly $70 a pound.

Wow! When I had my system refilled in 2006, the HVAC tech charged me $10 a pound for R-22! I had a 4 ton, 12 SEER system too.
__________________
FIREd is online now   Reply With Quote
Old 04-29-2013, 04:58 PM   #17
Full time employment: Posting here.
 
Join Date: Apr 2009
Posts: 731
For that price... what would a new unit cost? There used to be tax advantages to getting a new "efficient" appliance but I don't know if they are still there.
__________________
Retired July 2, 2010 at 62. My only regret is that I couldn't do it sooner.
thinker25 is offline   Reply With Quote
Old 04-29-2013, 06:34 PM   #18
Recycles dryer sheets
 
Join Date: Apr 2013
Location: Fishers
Posts: 385
wow - i replaced my entire 20 year old HVAC unit in Feb with a 96% efficient condensing gas furnace and 13 seer 3 ton A/C for less than $4500
__________________
wmc1000 is online now   Reply With Quote
Old 04-29-2013, 06:45 PM   #19
Thinks s/he gets paid by the post
 
Join Date: Jul 2012
Location: Mississippi
Posts: 1,878
Quote:
Originally Posted by FIREd View Post
Wow! When I had my system refilled in 2006, the HVAC tech charged me $10 a pound for R-22! I had a 4 ton, 12 SEER system too.
EPA has declared war on R-22, it supposedly has tripled in the last year to 70-90 /lb. I replaced a compressor in '11 and the whole job was ~$1300, hope it last another 10 yrs...

Supposedly there is R422D which is a direct replacement for R22

__________________
rbmrtn is offline   Reply With Quote
Old 04-29-2013, 06:46 PM   #20
Recycles dryer sheets
 
Join Date: Dec 2012
Posts: 390
Yeah, a 30lb can of freon now is almost $500. And to think it used to be so cheap, it was used to clean the coils.

Are you sure the compressor is running? Even though the fan is running, the compressor might not be.

BTW, here's <a href="http://www.diychatroom.com/">a diy chatroom that you might enjoy</a>
__________________

__________________
Elbata is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


 

 
All times are GMT -6. The time now is 12:39 PM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2017, vBulletin Solutions, Inc.