Old 10-03-2018, 06:58 PM   #1
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 11,815
EEs - X10 tripping ArcFault Breaker

I recently replaced my breaker box and to comply with the latest electrical code, I had to install a bunch of arc fault breakers. All is well, except one circuit. I have an X10 switch in one electrical box that can be actuated either directly or remotely, making it function like a 3 way switch. A second electrical box holds a regular switch (for a separate light) and the remote X10 actuator switch. I can turn on the light with the remote actuator switch with no issue if the other switch is off, but if the switch is on and I use the remote actuator switch, it trips the arc fault breaker. Both are on the same circuit. Prior to the arc fault breaker installation, all was good.

Some Googling turned up no answer, so I'm tossing it out to the EEs here who might have more insight.
__________________

__________________
You probably mean principal not principle. Judgment only has one "e".
travelover is offline   Reply With Quote
Join the #1 Early Retirement and Financial Independence Forum Today - It's Totally Free!

Are you planning to be financially independent as early as possible so you can live life on your own terms? Discuss successful investing strategies, asset allocation models, tax strategies and other related topics in our online forum community. Our members range from young folks just starting their journey to financial independence, military retirees and even multimillionaires. No matter where you fit in you'll find that Early-Retirement.org is a great community to join. Best of all it's totally FREE!

You are currently viewing our boards as a guest so you have limited access to our community. Please take the time to register and you will gain a lot of great new features including; the ability to participate in discussions, network with our members, see fewer ads, upload photographs, create a retirement blog, send private messages and so much, much more!

Old 10-03-2018, 07:01 PM   #2
Thinks s/he gets paid by the post
RobbieB's Avatar
 
Join Date: Mar 2016
Location: Central CA
Posts: 4,556
Me thinks the X10 triac noise is tripping the breaker
__________________

__________________
Retired at 59 in 2014. Should have done it sooner but I worried too much.
RobbieB is offline   Reply With Quote
Old 10-03-2018, 07:05 PM   #3
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
NW-Bound's Avatar
 
Join Date: Jul 2008
Posts: 25,789
Yes.

But I do not follow the OP's wiring of 2 X10's in a 3-way arrangement, and with a manual switch in the mix.
__________________
"Old age is the most unexpected of all things that can happen to a man" -- Leon Trotsky
NW-Bound is offline   Reply With Quote
Old 10-03-2018, 07:10 PM   #4
Thinks s/he gets paid by the post
OldShooter's Avatar
 
Join Date: Mar 2017
Location: City
Posts: 3,764
There is a non-dimming Decora style X-10 switch that uses a relay not at triac. You could try one of those. They make a pretty good "clunk" sound when they switch, though.

Actually, what I would probably do is to replace the breaker with a standard one. Just because the manufacturers successfully lobbied the NEC doesn't mean that these new breakers are critical to civilization's survival.
OldShooter is offline   Reply With Quote
Old 10-03-2018, 07:52 PM   #5
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 11,815
Quote:
Originally Posted by OldShooter View Post
There is a non-dimming Decora style X-10 switch that uses a relay not at triac. You could try one of those. They make a pretty good "clunk" sound when they switch, though.

Actually, what I would probably do is to replace the breaker with a standard one. Just because the manufacturers successfully lobbied the NEC doesn't mean that these new breakers are critical to civilization's survival.
I don't know what a triac is, but this is the device I have installed. It makes a thunk like a relay.


I can certainly swap out the arc fault breaker, but having $40 bucks in it, I'd like to get some value out of it if I can.
__________________
You probably mean principal not principle. Judgment only has one "e".
travelover is offline   Reply With Quote
Old 10-03-2018, 07:54 PM   #6
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 11,815
Quote:
Originally Posted by NW-Bound View Post
Yes.

But I do not follow the OP's wiring of 2 X10's in a 3-way arrangement, and with a manual switch in the mix.
The manual switch in the mix is incidental - for some reason the tripping occurs when this otherwise unrelated switch is on.
__________________
You probably mean principal not principle. Judgment only has one "e".
travelover is offline   Reply With Quote
Old 10-03-2018, 08:02 PM   #7
Thinks s/he gets paid by the post
RobbieB's Avatar
 
Join Date: Mar 2016
Location: Central CA
Posts: 4,556
If it is a relay, there will be arcing. Maybe bad relay?
__________________
Retired at 59 in 2014. Should have done it sooner but I worried too much.
RobbieB is offline   Reply With Quote
Old 10-03-2018, 08:28 PM   #8
Moderator
Jerry1's Avatar
 
Join Date: Nov 2014
Posts: 3,142
When I had that problem, there was a problem with the neutral. I’m no electrician but watching them try to figure it out was interesting. They kept saying everything tested out just fine, but every time I hit the switch, the breaker would trip. Finally, one guy said that the neutral was eff’d up, connected the wire better and all was well. Don’t know if that will help, but maybe double checking all the connections is in order?
__________________
Every day when I open my eyes now it feels like a Saturday - David Gray
Jerry1 is offline   Reply With Quote
Old 10-03-2018, 08:30 PM   #9
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
NW-Bound's Avatar
 
Join Date: Jul 2008
Posts: 25,789
Quote:
Originally Posted by travelover View Post
The manual switch in the mix is incidental - for some reason the tripping occurs when this otherwise unrelated switch is on.
What does that manual switch power, or is connected to?

It sounds like an extra load or capacitance on the Triac circuit changes the electrical noise characteristics, and that bothers the AFCI.

By the way, I have no experience with AFCI's, but have been studying this in order to have a safe installation of my DIY solar/storage system. DC arcing is A LOT worse than AC arcing.

Here's a video where a guy shows that his AFCI does not work at all.

__________________
"Old age is the most unexpected of all things that can happen to a man" -- Leon Trotsky
NW-Bound is offline   Reply With Quote
Old 10-03-2018, 08:32 PM   #10
Thinks s/he gets paid by the post
RobbieB's Avatar
 
Join Date: Mar 2016
Location: Central CA
Posts: 4,556
Yeah, a bad neutral would make for more noise. Before 3 wire, neutral was ground and it really still is. If you measure any voltage between neutral and ground you have a problem.
__________________
Retired at 59 in 2014. Should have done it sooner but I worried too much.
RobbieB is offline   Reply With Quote
Old 10-03-2018, 08:37 PM   #11
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
 
Join Date: Sep 2005
Location: Northern IL
Posts: 21,830
Quote:
Originally Posted by travelover View Post
The manual switch in the mix is incidental - for some reason the tripping occurs when this otherwise unrelated switch is on.
But if they had to connect/re-connect the wiring to that switch, maybe something got miss-wired? Could that other switch be shorting out something when the X-10 is activated?

I'm not following the connection of that other switch though. Just a thought.

-ERD50
ERD50 is offline   Reply With Quote
Old 10-03-2018, 08:42 PM   #12
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 11,815
Quote:
Originally Posted by NW-Bound View Post
What does that manual switch power, or is connected to?
The manual switch controls two overhead lights - one is a 4 foot fluorescent with a ballast transformer and one is an LED bulb.

Quote:
It sounds like an extra load or capacitance on the Triac circuit changes the electrical noise characteristics, and that bothers the AFCI.
............
Yea, I'd say so. I was hoping for a trick to make them compatible.
__________________
You probably mean principal not principle. Judgment only has one "e".
travelover is offline   Reply With Quote
Old 10-03-2018, 08:42 PM   #13
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
NW-Bound's Avatar
 
Join Date: Jul 2008
Posts: 25,789
OK. While we are on the subject of "electrical arcing" and the associated danger of fire, y'all may find the following interesting, and you do not even have to be an EE.

That is, DC arcing is a hell of a lot scarier than AC arcing, as this fellow demonstrates. He shows that 2.6kW circuit causes a hell of an arc with DC power. And I am building a 4.5kW solar system. Of course I have to be very very careful and have to know what I should know.

__________________
"Old age is the most unexpected of all things that can happen to a man" -- Leon Trotsky
NW-Bound is offline   Reply With Quote
Old 10-03-2018, 08:50 PM   #14
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
NW-Bound's Avatar
 
Join Date: Jul 2008
Posts: 25,789
Quote:
Originally Posted by NW-Bound View Post
... It sounds like an extra load or capacitance on the Triac circuit changes the electrical noise characteristics, and that bothers the AFCI.
Quote:
Originally Posted by travelover View Post
The manual switch controls two overhead lights - one is a 4 foot fluorescent with a ballast transformer and one is an LED bulb.

Yea, I'd say so. I was hoping for a trick to make them compatible.
There might be some weird interference between the X10 triac and the LED bulb.

Do you remember ERD50's experience with a light dimmer (there's always a Triac in one) and an LED bulb that flickers until tamed with an incandescent in parallel?

You would need to look at the AC waveform with a scope. Or maybe a spectrum analyzer, as I understand that AFCI's look for a certain frequency characteristic to detect arc fault.
__________________
"Old age is the most unexpected of all things that can happen to a man" -- Leon Trotsky
NW-Bound is offline   Reply With Quote
Old 10-03-2018, 09:06 PM   #15
Thinks s/he gets paid by the post
Souschef's Avatar
 
Join Date: Dec 2015
Location: Santa Paula
Posts: 2,551
I had a wired one some time ago. For no apparent reason, the monitor on my PC would blink off, then come back on.
I finally discovered the when DW turned off the ceiling fan in the bedroom which backs up to our office, it generated enough EMI to affect the monitor The light switch on the same circuit did not affect the monitor.
__________________
Retired Jan 2009 Have not looked back.
AA 50/45/5 considering SS and pensions a SP annuity
WR 2% SI 2SS & 2 Pensions
Souschef is offline   Reply With Quote
Old 10-03-2018, 09:17 PM   #16
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
HFWR's Avatar
 
Join Date: May 2005
Location: Lawn chair in Texas
Posts: 13,964
According to the description, this x10 device is a relay/non-dimmable, so no triac...
__________________
Have Funds, Will Retire

...not doing anything of true substance...
HFWR is offline   Reply With Quote
Old 10-03-2018, 10:03 PM   #17
Give me a museum and I'll fill it. (Picasso)
Give me a forum ...
travelover's Avatar
 
Join Date: Mar 2007
Posts: 11,815
Quote:
Originally Posted by ERD50 View Post
But if they had to connect/re-connect the wiring to that switch, maybe something got miss-wired? Could that other switch be shorting out something when the X-10 is activated?

I'm not following the connection of that other switch though. Just a thought.

-ERD50
I changed out the breaker box with the help of an electrician. All we did was pull out wires from the old breaker box then reconnect them to the new box. The problem seems to be erratic - so maybe it is as simple as a bad connection.
__________________
You probably mean principal not principle. Judgment only has one "e".
travelover is offline   Reply With Quote
Old 10-04-2018, 12:22 AM   #18
Thinks s/he gets paid by the post
Telly's Avatar
 
Join Date: Feb 2003
Posts: 1,688
Quote:
Originally Posted by NW-Bound View Post
OK. While we are on the subject of "electrical arcing" and the associated danger of fire, y'all may find the following interesting, and you do not even have to be an EE.

That is, DC arcing is a hell of a lot scarier than AC arcing, as this fellow demonstrates. He shows that 2.6kW circuit causes a hell of an arc with DC power. And I am building a 4.5kW solar system. Of course I have to be very very careful and have to know what I should know.
Back in the 1970s I needed to quickly design a 48 volt DC battery backup system for a system product. Batteries, equalizer charger, battery disconnect relay and controls including low voltage lockout and a system needs to shut down now trigger in advance of battery minimum.
There were some things that could be done to minimize arc on break, like magnetic blowouts, speeding up the rate of contact break by using a DPST relay and wiring the two contacts in series, effectively doubling the opening rate. Since then, I think there have been major advances in high-current contact metallurgy.
__________________
-- Telly, the D-I-Y guy --
Two fools dancing on the hands of time
Telly is offline   Reply With Quote
Old 10-04-2018, 03:00 AM   #19
Thinks s/he gets paid by the post
gauss's Avatar
 
Join Date: Aug 2011
Posts: 2,586
Quote:
Originally Posted by Telly View Post
Back in the 1970s I needed to quickly design a 48 volt DC battery backup system for a system product. Batteries, equalizer charger, battery disconnect relay and controls including low voltage lockout and a system needs to shut down now trigger in advance of battery minimum.
There were some things that could be done to minimize arc on break, like magnetic blowouts, speeding up the rate of contact break by using a DPST relay and wiring the two contacts in series, effectively doubling the opening rate. Since then, I think there have been major advances in high-current contact metallurgy.
Wow! I thought that an inductive load (ie coils, motors etc.) was necessary to get the significant arcing shown in the video.

The heating coil load appears to be mostly resisitive (ie very small inductance).

I guess that I might need to retest for that 'EE' degree granted 30 years ago - or remember that I am not an electrician!

-gauss
gauss is offline   Reply With Quote
Old 10-04-2018, 11:29 AM   #20
Full time employment: Posting here.
bjorn2bwild's Avatar
 
Join Date: Mar 2013
Location: Western US
Posts: 894
When an answer is not easily had, a little experimentation can often shed some light.

Progressing from more to less likely and easy to hard.....swap the LED light for incandescent, same with the fluorescent if practicable, swap the switch with another, ditto the breaker.
__________________

bjorn2bwild is offline   Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fat Fire-ees - are you out there? DawgMan FIRE and Money 188 09-29-2019 03:11 PM
FIRE-ees: any regrets? Lusitan Life after FIRE 31 04-13-2007 10:19 PM

» Quick Links

 
All times are GMT -6. The time now is 04:07 AM.
 
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2019, vBulletin Solutions, Inc.
×